  1. sslobodan

    Grounding resistor

    High Resistance Grounding (HRG) systems limit the fault current to such a low value that the breaker does not have to trip and the loads continue to function without interruption. Best presentation I found on net is on site www.i-gard.com you can Download everything you need to have arguments...
  2. sslobodan

    CT Earthing (grounding)

    As Slava said it is only for a protection or to be precise by grounding CT you get the currents maximized at 1.7 of nominal. I can search over on my papers for detailed explanation of this but I believe that this satisfies as an answer to your question
  3. sslobodan

    Siemens USA Website - Just Venting

    My sister works in Siemens in sales and even she has the problem handling the informations she needs. She works in Europe and that should say about the organization of company. Siemens is Huge, a giant and I doubt that ABB can buy it, it can only merge. In principle when I look for specific data...
  4. sslobodan

    Column Type Voltage Transformer-50 Hz

    I guess that all major producers have it but if you want one name its Siemens and you have it all over the world, so you don't have to search too much for it. (Also check GE, ABB, Schneider...)
  5. sslobodan

    480V power wiring: wiring from hot to ground to get 277V - OK?

    One addition this means that you need to have symmetrical 3 phase system at beginning so you can have neutral point (star) on it grounded, and I suppose you have symmetrical system.
  6. sslobodan

    480V power wiring: wiring from hot to ground to get 277V - OK?

    If you need a neutral you need to create one. It is simple system. You ground a starting neutral point for entire system and than run neutral around where you need it. You should not ground neutral on some other place and you should not connect grounding to neutral at any other place. This is...
  7. sslobodan

    Transformer commissioning and testing

    I would disagree with short circuit test on a second hand transformer for more than 0.35s unless you have a chance to get it back to the supplier if it fails on the test. I remember one story from my lectures. My professor was hired to test some transformers built for the 600MW power station...
  8. sslobodan

    Earthing or Grounding

    Well for start before you can ask your self what is the maximum value of the grounding resistance you must ask why do you put it at all? Most of the people meet grounding as another boring requirement from the law, but it has a great value. By definition grounding is put to make shortest path...
  9. sslobodan

    Who can rent me a 230/22 kV, 15MVA transformer?

    Well try to buy used transformer and sell it after you don't need it as used transformer, with copper prices rising you would be able to earn some money on it in stead of loosing it. Lease would be very expensive because if If anyone had a transformer on side he would like to pay back that...
  10. sslobodan

    Transformer commissioning and testing

    First you should ask for their maintenance data to look what problems they had. In general you should look how they react at over current/over voltage, and that transformers should withstand 120 % load for few hours, 160 load for 15 minutes. You use thermal vision for determining are the...
  11. sslobodan

    an IEEE or ANSI standard phase shift of 30 degrees

    There is a phase shift between transformator sides that is equal to a n*30 degrees where n is whole number. n is called hour number and is usually mentioned on the nameplate. This is definition of the hour number for transformers, It goes in all European standards, so I believe it sounds the...
  12. sslobodan

    10kV 50Hz DG sets

    You have cat and Leroy Sommer in China. Try to find there representatives.
  13. sslobodan

    Calculating 120V loads on 208/120V system

    you are calculating 3+3+4 single phase load by taking 4 for all. It goes for cable calculation but not for consumption. Your consumption is 10*500W/120V + (5*500W)/(1.73*208V) This means one phase will have load of 24 A while rest 2 will have current of 20A. For a equipment choosing you...
  14. sslobodan

    unstable machine

    You know that all cables going from VFD must be shielded, and that connection should be as short as possible?
  15. sslobodan

    Conductor's Insulation Material Types

    http://www.helukabel.de/index.php?lang=en http://62.180.125.140/cms/en/webkatalog/katalogeinstieg_aufzugs_und_foerdermittelleitungen_ausgleichsleitungen_oelflex_lift/1/index.html they have their cable pictures so you can have an idea how does the cable look like, and a pretty good explanation...