Hi there,
Some of the traditional methods for reducing arc-flash is to have to bus differential protection for quicker tripping and at times reducing incident energy on the bus.
Now, as far as I know, most of the electrical softwares (EasyPower, ETAP and SKM) allows you to model only...
Hi there,
What are the standard formulaes used in desiging an outdoor 44kV current limiting reactor in a substation. Downstream of the reactor is a solidly grounded 44/26kV, 10MVA distribution transformer. Happy if someone could refer me to a section of a book, IEEE or CSA standard?
The...
Hi all,
How do I calculate the capacitance for a oil-filled transformer and power factor correction capacitor bank. Any reference to texts or IEEE standards will be helpful.
Thanks.
Sonic 02
Hi,
Typically the requirements of the type of relays would be dependent on the Owner. They may have some standards preference for relays of a specific manufacturer. If it is older substation with no source of DC supply, it maybe using electromechanical relays. The protection design needs to...
Hi All,
I'm adding four(4) new, 15kV metal-clad switchgear breakers to an existing line-up. I plan to utilize DC power for the tripping, closing, spring-charging and protective relay. Now, my concern is whether the existing battery cells have the adequate capacity (i.e. battery voltage)to...
Hi Sanjay,
The Canadian Code states that for direct buried cables in a trench , you will need a minimum of 1000mm of separation from the top of the conductor to the finished grade level for this voltage class.
Now, if you have some form of mechanical protection (i.e. wooden planks) in your...
Hi All,
First question:
We have a new 500kVA, 13.8kV/600V dry-type ventilated transformer to be installed in a new electrical room. The dimensions of the electrical room is sufficient so real estate is not a concern here. My main concern would be the most ideal location of the transformer...
I would go with a DC system for charging the breaker spring operating mechanism. A battery bank (eg 125Vdc, 60 cells) may be used to feed a DC panelboard which is being utilized to provide a DC supply for motor spring charging.
sonic02
Hi there,
There are certain considerations you will need before choosing the right switchgear or disconnect switch for your application. The primary function of the switchgear is to isolate faulty equipment, to reconfigure networks in order to restore power supplies, to divide large network...
Hi All,
We are planning of installing three(3)- single-phase,25kVA, 13.8kV/600V, pri- Delta and sec- wye-grounded pole-mounted transformer for our system. For protection on the primary-side of the transformer, I was wondering if I should spec out a self-protected transformer in which the surge...
Hi there,
Can you run 1kV,teck 90 3C#1 AWG power cable, a 4/0 AWG grounding conductor and Instrumentation Cables (in a 4" rigid PVC conduit) in the same trench as mechanical hot and cold water pipes?
Sonic