Recent content by slavag

  1. slavag

    Arc detection relay Vs UFES (Ultra fast earthing switch)

    Arc detection relay send close command to UFES. You need both of them.
  2. slavag

    Kingsine or other brand relay test kits

    We use three types of Kingsine. One is simple, old type. One is small size KFA300. 3 currents, up to 10A , 3 voltages... 3.6kg, with display, touch screen. A last device, 6 currents, 6 voltages. KF86P with display, touch screen. Good devices, good price.
  3. slavag

    Power Transformer 300/150/150MVA cooling type.

    Dear PRC Thanks a lor for your help!
  4. slavag

    Power Transformer 300/150/150MVA cooling type.

    In case of ONAN/ONAF we use 0.6..0.7/1 Sonan / Sonaf. What is recommendation for ONAN/ODAF?
  5. slavag

    78V/Vector Shift/Voltage Surge/Vector Surge protection in the Distribution Generation system

    Dear Colleagues. What is experience with this type of anti-islanding protection? What is regulation/standards in your system. Thanks in advance
  6. slavag

    Power Transformer 300/150/150MVA cooling type.

    Dear Colleagues. What is preferable cooling type of Power Transformer 300/150/150MVA 161/33/33kV? It will be Step-Up transformer. Generation type : PV and BESS. ONAN/ONAF ONAN/ONAF/OFAF ONAN/ONAF/ODAF Thanks a lot in advance!
  7. slavag

    Parallell CT for 7UT86

    yes, it is standard solution for years
  8. slavag

    YNd11 (earth fault at delta side)

    59N, residual overvoltage protection (broken delta, voltage displacement, etc.) But, it is common detection for whole system. You can use Varmetric, IosinF0 for feeder detection.
  9. slavag

    Earth mat design Using ETAP software for Industrial substation (High Short current Fault)

    Good explanation of erdep!!! Saiedsadat, take in account, 400V is solid ground. important point: EN 50522:2010 Earthing of power installations exceeding 1 kV a.c.
  10. slavag

    Earth mat design Using ETAP software for Industrial substation (High Short current Fault)

    Do not need make such calculation in the 400V level with TNS system. Earth current is back via PEN. You have calculated on the 20kV side only.