Hi SAK9
Thank you for your reply..
Your opinion is logic and right I have only one generator operate.
I've got information from the generator specialist, the flexible rubber joint always broke because it can't handle the pressure from discharge pump (Plate Heat Exhanger actually only 6 bar) and...
Hi all..
I am sorry for late response..
@Littleinch
I solved it with the help from the generator specialist, he calculate and select the Plate Heat Exhanger based on our requirement data.
I just do the rest..Thank you..
Hi all..
Can someone explain to me in technical/engineering, what should I consider and the effect, if :
1. I put the pumps in "parralel position" with header to inlet side of PHE.?
2. I put the pumps in "parralel position" with header to outlet side of PHE.?
3. I put one pump to one PHE and so...
Hi all..
Thank you for respon my thread..
I've solve this problem..
@Littleinch..
Thank you for your help.
Maybe my data for you is unbelievable but I've got the data from the brochure.
I am sorry,I can't posted the data because I've only the hardcopy..
Hi All..
@Artisi
Yes, it is.. I've done create simple system and Plate Heat Exhanger data after followed other similiar project. Finally, my boss said, our job scope do not need include the Water Cooling. Only, Plate Heat Exhanger and the pipe dimension and line.
@MintJulep
I don't know the...
Hi all..
I add some information, such as:
1. Coolant capacity without Radiator (liter) = 170
2. Ambient air temperature (Degree) C = 40
3. Maximum Head Static of Coolant (ft) = 32.8
4. Maximum Outlet Pressure of Engine Water Pump (psi) = 28.6
5. Heat Rejection to Atmosphere from Engine (kW) =...
I agree with dbill74..
The basic for select louver size is CFM
You can follow dbill74 information, or you can estimate it.
CMH = Area x Floor to Floor Height x Air Change/hour
CFM = 1.69 x CMH
Then,
you can used catalog for louver selection.
Thank you all, for reply my thread..
@GroovyGuy
The radiator function have been change with Cooling tower/Water Cooler.. I'll check and inform you about the ambient temp.. I am newbie about generator/genset, but my job scope is HVAC => PHE (Plate Heat Exhanger) and Cooling tower..I got...
Hi all..
I have no idea how to calculate PHE flow and temperature for Cooling tower. The objective are selecting PHE and cooling tower for genset for my design..
If :
- Genset capacity : 2000 kVA
- Genset heat rejection to coolant : 60816 BTU/min
- Coolant Flow : 436 GPM
- Standard Thermostat...