Thank you jmw, you finally got my drift. We have a 25 years old centrifuge process (26 birds all together in parallel configuration). They are used to centrifuge raw bitumen (oil sand industry) to remove solids (5 to 10% fines). Right now we don't have any kind of instrumentation on the process...
When dealing with steam application it is important to protect the transmitter from possible over temperature conditions. The best way to do this is to take the impulse piping out the side of the process piping into the outlet of a Tee. Another steam transmitter installation I did in the past...
By the sound of it, I think the problem is the dowstream piping has a long run and in upward direction. This will cause your valve to cavitate because of downstream pressure build up caused by high mixed phase velocity. Of course it does not help when the size of the valve is less than 1/2 of...
I would recommend, Liptak (Process Control), Fundamentals of Industrial Controls, Continuous process control, and understanding distributed process system for control. These are good reference books and are available from ISA.
Steam DP transmitter tubing should slope downwards toward the DP cell and include a "dead leg" or pigtail.If either the condensate levels or both legs of DP cell can not be kept at the same height, the difference in elevation (levels or diaphragms) will cause a DP offset that must be compensated...
As a general rule "control valves and abrupt enlargements must be installed an adequate distance downstream of the flowmeter to minimize downstream pipe effect"
Hello everyone,
I am interested in instrumentation used to automate these type of centrifuges, especially in mining industry. If you have any first hand experience with them please write back. I am particularly interested in Bird's centrifuges. I have found very little information on their...
Hello everyone,
I am interested in instrumentation used to automate these type of centrifuges, especially in mining industry. If you have any first hand experience with them please write back. I am particularly interested in Bird's (manufacturer) centrifuges. I have found very little information...
I am interested in instrumentation used to automate these type of centrifuges, especially in mining industry. If you have any first hand experience with them please write back. I am particularly interested in Bird's centrifuges. I have found very little information on their actual design and...
"BE" or "BA" stand for Burner Element and Burner alarms respectively.
At our plant we use "BSE" for burner safety element or BE, BI or BM for Burner elemnt, Burner indicator or Burner Scanner.
All the gas detectors and alarms are designated as AIT or ASH etc for analyzers.
Thanks
The only way I know to do it is via Hart Modem, available from emmerson (rosemount), and AMS (asset management suit) software. I don't know if Hart modem can work stand alone or you need complete package. Ask your nearest sales rep. The demo version of this package will cost approx. 1500 - 2000...
SAFCON It's Your Call
A control valve can be used in lieu of a separate safety shutdown valve for SIS applications. One technique is to install a solenoid in series with the valve positioner, downstream of the positioner output. The solenoid valve is operated by a SIS signal when a process...
ISA-S84.01 section 7.4.3.1 specifically prohibits the use of a control valve from the basic process control system (BPCS) as the only final element for SIL 3. It goes on to say, "A safety review shall be required to use a single BPCS control valve as the only final element for SIL 1 and...