  1. SA07

    To replace obsolete Mark VIe steam turbine control system

    Hi Spares for the Mark VIe are becoming obsolete. For a 45 MW steam turbine , what other control system we can use instead of Mark VI? The system is very complex, the spare cards are very expensive and very long delivery delay. Can we replace with Woodward or another system?
  2. SA07

    To replace faulty power alternator with a smaller unit

    Waross: We do not have this system of motoring the alternator at start up. To start up, we run on barring gear for some time and then increase the speed of the turbine through a ramp defined in the PLC by opening the control valve and supplying steam from the boiler until nominal speed and then...
  3. SA07

    To replace faulty power alternator with a smaller unit

    Hi Waross Is it not the opposite i.e. the turbine that provides the mechanical energy to drive the alternator?
  4. SA07

    To replace faulty power alternator with a smaller unit

    The turbine and gear remain the same. They will be connected to a smaller alternator of size 46 MVA. Output of gear speed to the alternator is the same i.e. 1500 rpm
  5. SA07

    To replace faulty power alternator with a smaller unit

    Hi Due to breakdown of an alternator 60 MVA, can we replace it with another alternator 46 MVA? We intend to replace only the alternator; the gear and turbine will remain the same. Please see details below Bigger plant...
  6. SA07

    Lifetime of Fire trace tubing

    Hi We have Firetrace system installed in our electrical panels since 2017. Some piping are starting to crack. All our electrical rooms are clean, air conditioned. Have any one encounter this issue? Any idea what is the lifetime of the Firetrace tubing? Thanks
  7. SA07

    Turbo alternator tripped by reverse power

    Hi We have 2 turbo alternator exporting to utility grid. One turbo alternator tripped by reverse power and generator breaker opened. From fault recorder, we do not see a big fault or disturbance on the network. Feedback from Utility: they were switching flow of power to another substation. Any...
  8. SA07

    Lightning protection of power plant

    Thank you FacEngrPE for detailed explanation and links
  9. SA07

    Lightning protection of power plant

    Hi We are a power plant. Since construction, lightning rod were installed on the boiler, substation 66 kV, lightning arresters on 66 kV lines and earth cables over 66 kV transmission lines. Over time 2 additional small power plants were constructed. They are not sufficiently protected against...
  10. SA07

    Ultrasound testing of MV/HV equipment

    Hi Does someone has a table showing the acceptable levels of ultrasound when doing this test? Are there any standards for these test e.g. IEC? Thanks
  11. SA07

    Can we operate Emerson Scada system/Server with Siemens PLC 400 ?

    Hi We have a Siemens Scada system, 2 servers, 1 process historian. We intend to renew this part as we are having some issues with 1 server. It was renewed in 2015 and previous system installed in 2007. We have 2 power plants exporting to national grid. We belong to an international group which...
  12. SA07

    Can we replace an AVR Basler 250 with Basler 200?

    Hi There are Basler 250 on 3 hydro plants. We have 1 spare Basler 200 in our store for another turbo-alternator. Can the hydro plant replace their Basler 250 with Basler 200 in case of breakdown?