Article "Bonding with signal reference grids" EC&M, December 1, 1999 has the following recommendations:
"The AC current on any portion of the SRG should not exceed 250mA. AC current exceeding this level will cause voltages that can affect data signals.
• Measure the equipment-grounding...
The grounding infrastructure shall be in compliance with IEEE Standard 1100, TIA-942 and TIA-607 requirements.
See article G.5.1.6 of TIA-942 for the particular equipment bonding requirements.
Please review the attachment.
Best regards.http://files.engineering.com/getfile.aspx?folder=76e9c4e2-dc27-47c4-a361-840c846a8619&file=Generator_ground_fault_relay.pdf
The UTP cable should be installed some distance away from an EMI sources. Cabling pathways standard, EIA-569 table 4.8-5 provides those guidelines (source LANs/cabling-faq that refers to Northern Telecom, doc # IBDN-UM-9105, 1991):
Minimum Separation Distance
from Power Source...
Please review the attached file which shows the neutral bonding requirements.http://files.engineering.com/getfile.aspx?folder=a1f0c66d-41ab-483b-bbd3-ca4967784394&file=ATS_Generator_grounding.pdf
Please see the attached article.http://files.engineering.com/getfile.aspx?folder=7ad3b70e-cf68-4292-8d12-748f04a91a71&file=Reverse_feed_transformer.PDF