Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by reactive

  1. reactive

    CB model for switching studies

    Hello all I am modelling a VCB for transient studies and am a little confused. IEC62271 prescribes TRV tests on a 36kV breaker at a TRV rate of rise of 0,57kV/us, however the literature suggests that when modelling the VCB withstand a value of between 20-30V/us should be used. This is very...
  2. reactive

    Can you overload an alternator

    Please can you help me understand something. In the 4x4 world we often install a second battery in a vehicle to power fridges etc. This is normally connected to the charging circuit via an solenoid when the engine runs. If the second battery is very flat a very high charging current could flow...
  3. reactive

    Star/star or star/delta

    Haven't been on the forum for a long time. Hoping I can get some advice. A client is designing a network for a mine. The supply transformers are 2 x 80MVA 132/33kV Yd earthed via a NECR. The 33kV is required due to the heavy load and can be considered as an intermediate voltage. The mine and...
  4. reactive

    Undervoltage protection

    Thanks guys. There are undervoltage relays currently installed on the winders. Problem is that they are tripping spuriously due to dips. Relays are set to 80%Un instantaneous and I was wondering if it would be good practice to recommend a time delay to offer better dip ride through. Question is...
  5. reactive

    Undervoltage protection

    I am trying to find 'typical' undervoltage settings for a SCIM. I have very few details on the machines (they are pretty old) apart from 4MW, 6,6kV and application ward leonard mine winder. I don't want to pre-empt but would imagine an UV level of 80%Un would be acceptable (yes/no? lower?) but...
  6. reactive

    Point on Wave Switching for Capacitor Banks

    Sorry I am late in on this one, haven't been in the forum for some time. POW switching would be for energising transients on a cap bank/filter bank. The initial voltage collapse is given by dV=Ls/(Ls+Lf); where Ls = source inductance and Lf = filter inductance. For a large bank such as b4l's...
  7. reactive

    RC failure

    Here’s the problem : Network : - 132/6,6kV 20MVA 10% Yd (earthed via NECR) supply transformer, giving LV fault level of 192MVA. - 6x6,6kV 150mm^2 400m PILC feeders to Mill Substation. Mill SS feeds 2 x 5,5MW mills. - Speed control is achieved by slip recovery via Alstom PWM drive in rotor...
  8. reactive

    Fault Current Contributions of Harmonic Filters

    Correct, contribution is negligible and can be ignored.
  9. reactive

    Switchgear Fault Level

    In answer to your question regarding the 30kA for 3s. This is simply the rated short time current of the of the board (busbars etc.). The amount of current that the board can handle depends on the duration of the fault i.e. k=I^2t = 2700kA^2s. If the max. fault duration was 2s then rated short...
  10. reactive

    EAF transients

    Client has been having irregular 11kV VT failures on an submerged arc furnace installation. System details as follows: - 2 x VTs per furnace 11/28/75kV connected phase to phase upstream of the furnace breaker. - Supply transformer 88/11kV 75MVA. - 4,8 MVAr plain capacitor bank switched with the...
  11. reactive

    Over Current protection time grading

    We generally set the pickup on the HV at 200-250% full load to avoid nuisance tripping due to inrush and the LV at 125% to provide some overload protection. However, as Bung alluded to above, we find that one generally runs out of time when doing grading. Protection across transformers and...
  12. reactive

    123 kV Capacitor bank connection

    All transmission banks on our network are connected double star. Only delta connections I have seen are at LV.
  13. reactive

    Ferroresonance

    From the above I must conclude that the risk of ferroresonance is acceptably low, for the following reasons: - Earthed system. - 3 phase switching (no grading capacitors). - Capacitors not switched with transformer (although they could obviously be tripped with the transformer). Must sound like...
  14. reactive

    Ferroresonance

    Is it possible for ferroresonance to occur in the following scenario : 22/11kV 2MVA Dyn transformer, resistance earthed, no load on transformer. 1,1 MVAr plain capacitor bank connected at 11kV. My understanding is that for ferrorresonance to occur there must be either an unearthed system or...
  15. reactive

    Failure of Power Factor Correction Capacitors

    Sorry to come into the discussion so late. With one 10 MVA transformer in circuit resonance occurs near to 11th/13th which may be a problem depending on the harmonic sources on the network (you do mention traction nearby) especially as there is often no damping load. However if the transformers...

Part and Inventory Search