    Isolated neutral - Ungounded system - Earth fault calculation

    One other aspect that will come into focus is how you connect your current transformers to measure the fault current. A protection single line diagram would help understand the the co-ordination requirements
  2. PUNGLU

    REF protection for Transformer LV windings

    I wonder too how the 5 CT scheme is implemented. Do you mean to include an ICT?! There has been a shift towards low impedance schemes
  3. PUNGLU

    METERING CHANGE OVER.

    I agree with Scottty that no work is more important than human life.... But why not try this:- Change the supply to the feeder on breaker A. Go the source of B and shift the cable terminations as below: Y to R R to B B to Y In doing this you shift the voltages +120 degrees according to your...
  4. PUNGLU

    METERING CHANGE OVER.

    The change-over may work but consicer the commercial losses when the contactor fails. Before one get to discover the utility company may have lost quite some KWHrs.. A seperate meter may be the best solution commercially
  5. PUNGLU

    Power System Analysis

    With your single line diagram you will of course have sensing/relaying points. You must have the: i) muximum fault currents for faults at these points ii)minimum fault currents for faults at these points iii) muximum through fault currents at these points These basics plus all that you alredy...
  6. PUNGLU

    LOW VOLTAGE

    Thank you. I thought the PFC could be injecting more VARs. I have to liase with the client to carry out the above checks. I will give you feedback soon.
  7. PUNGLU

    LOW VOLTAGE

    We have a client metered on 11kV. From the breaker, the client has a breaker which switches on a 1.5MVA transformer on to a 415V bus. The client has a power factor correction capacitor bank of 500KVA and the loading is mostly inductive. The client has been complaining of high voltages between...
  8. PUNGLU

    Undervoltae relay and earthfaults detection

    Thank you guys!! I managed to get the manual and marshall the outputs to trip for an overvoltage. The scheme works very well.
  9. PUNGLU

    Can energizing a transformer cause the ground fault to trip

    I had an almost similar problem when a genset breaker tripped on energizing a transformer. I think it may be inrush since I dilayed the operation on inrush a few more cycles and the problem was solved.
  10. PUNGLU

    Undervoltae relay and earthfaults detection

    I would like to use the overvoltage function as to detect the zero sequence residual voltage and be able to trip the breaker on the trafo LV side. The relay, 7RW6000-2EA00-0DA00/BB, seem trip only on the undervoltage function. It can detect and annunciate an overvoltage but I cant get the...
  11. PUNGLU

    Undervoltae relay and earthfaults detection

    Yes, the VTs are positioned between the trafo and the autorecloser. There is a possibility of V connection and the broken delta connection. They are single phase units and I acn be able to connect them to suit my needs Thank you
  12. PUNGLU

    Undervoltae relay and earthfaults detection

    Hallo guys, need help on the 7RW6000 undervoltage relay. Can this relay be connected on the delta side of a Star/Delta transformer to detect eartfaults in the transformer when the Delta side autorecloser is open. Regards, Punglu
  13. PUNGLU

    7SJ6021 SIEMEMS feeder protection relay

    Any one with a soft copy of the above relay to avail it please. I am working on one and been googling to no avail. Thanks
  14. PUNGLU

    High Impedance Differential protection

    It is obvious that technological advancements have enabled manufacturers to come up with relays with less VA requirements. Low impendance differential and REF schemes are gaining popularity but a change from the high impedance could be purely based on economic sense. From the merits and...
  15. PUNGLU

    FLASHING ON A METERING CB

    We have undertaken studies on the cause of flashing on a yellow phase spout. The latest having destroyed the 11kV indoor CB. The CB was installed for a client whose load is mostly compressors, airconditioners and freezers. What could be the likely causes and what remedies do you suggest. This is...