The Main switchboard is 13.KV S&C Fusible disconnect switch with Source Transfer controller for Manual OR Automatic Transfer scheme
I have 13.8 KV Grounded - WYE Utility incoming Power on main distribution switchgear.
On site Generator is 480V/277V WYE Stepped up to 13.8KV using 480/277V...
1) jghrist - Neutral and ground are bonded only 1 place at transformer not at BESS
2) che12345 - Thanks for detail response!
2) a) The 1600A frame breaker has 800A Sensor plug and Ground fault pick up setting is 160A verfied. Upon trip breaker indicates reason for trip is Ground...
We already discussed this with BESS system manufacturer the quality of output from inverter supply is tightly monitors before the inverter is connected to Power system.
We have a 2.5 MVA 13.8KV (Y-G)/ 480V (Y-G) Utility power supplying power to Schneider Electric 4000A, 480V, 3 Ph, 4W QED6 Main Switchboard with MTZ breakers.
Building major loads Panels and other DG Sources are connected to this Main switchboard bus with their respective breakers.
One of the...
To all my learned colleague uninamously rejected Bolt-down bollards on asphalt surface. What is your opinion of using Pour in Place Bollard would that give better protection for pole mounted equipment as described...
I work in solar industry with carport canopy structure with pole mounted electrical equipment such as Solar inverters, AC combiner Panels with underground conduit risers at the canopy structural columns. The surface of these Carport is finished with asphalt. Bolt down Bollards are the cheapest...
My question is 2 part - for field installation electrical switchgear equipment multiple cubicle line up (Each cubicle typically 30 - 36 or 42 Inches wide + 90 in H X 54 in Depth weighing 1500-2000 lbs each.
If the switch mounting foundation floor is not prefectly levelled does manufacturers...
Thanks colleagues for your aanswers - The size of cable is 3#1/0 + GND in 4 "C I thought using LBs would solve the issue of bending radius. Once we use LBs The cable is 15KV, M105, Unshilded. Any comments?
What is the acceptable Electrical installation practice for Medium voltage 13.8 KV Switch enclosure feeder cables conduit entering from the Side of the enclosure instead of bottom.
Please see attached Photo. The contractor installed the UG conduits for 13.8 KV Feeder about 18 Inches outside the...
Does anybody have noticed the use of Current limiting Fuse (CLF) does not change available short circuit current results on the load side of the fuse performing ETAP short circuit study but then what is the explanation for the CLF does reduce the Peak let through current and short circuit duty...
Dave thanks for the suggestions. I saw Schneider Electric specifies Current limiting fuses or line reactors specific to each of their drives - I am not sure Rockwell international or other US drive manufacturers provide such recommendations...