Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by patrick7

  1. patrick7

    Underground VS Overhead Transmission lines

    thank you all so much for your replies.
  2. patrick7

    GFCI Breakers tripping

    just a thought here. i have seen this one strand on the conductor wire was not landed correctly and allowed a path for the leakage to trip the breakers. sorry i didnt remember that earlier.
  3. patrick7

    GFCI Breakers tripping

    sounds simple to me, nothing pluged in = defective.
  4. patrick7

    Underground VS Overhead Transmission lines

    Differences in protection systems and practices of the protection on overhead vs undergroud transmission lines. any thought anyone.
  5. patrick7

    Transformer vault installation

    there are companies that manufacture oil containment pits with sumps that trap the oil and allow the water to leave. might want to to a search for oil containment enclosures. i will look for the flyer that i had. not sure where it got to.
  6. patrick7

    Three Winding 132/11/11kV transformers

    could you please go into more detailed explanation? thx
  7. patrick7

    SS URD Transformer Corrosion Failure

    Sounds like the installation of some sort of cathodic protection may be in order. I am not exactly sure (it has been a lot of years) but I believe that one tenth of of a milli amp will plate out seven pounds of cu. in a year. I would look into protecting your investment.
  8. patrick7

    If you weren't an engineer, what would you be?

    Explosives Demolition Heavy Equipment Construction If you can't build it, break it Now that is either initial susess or total failure.
  9. patrick7

    xfmr loading

    Also, what is the rating of the transformer high and low side voltage? Also, what are the actual voltages impressed on the trasformer? PF of the load would be very helpful. also, is the transformer physically located in an area that does not allow for ample airflow for cooling? What are the...
  10. patrick7

    CT turns ratio

    The turns ratio of the transformer tells you how the current is going to be changed. The ratio of 100/5 is the nominal turns ratio. On large power bushing type transformers the primary turn is one. So for a ratio of 100 to 5 or 20 to 1 the secondary would need to have 20 turns. This say when...
  11. patrick7

    Power System Stabilizers

    I am trying to locate some information on the testing of power system stabilizers i.e. there are procedure to test PSSs but i was wondering if anyone has come accross any generic test forms that may be in the public domain. Thank you
  12. patrick7

    Motors and Starters Burning

    I agree with these previous posts on this problem, I would install a portable fault recorder and set the trigger levels to capture everything with a slight drop in voltage. Then retrieve the events from the recorder daily and look at the waveforms these will tell you exactly what is happening...
  13. patrick7

    Magnetic Clearances Around Reactor Banks

    scottf thank you very much that information is very helpful.
  14. patrick7

    Magnetic Clearances Around Reactor Banks

    Great, thank you for the information
  15. patrick7

    Magnetic Clearances Around Reactor Banks

    sorry about the lack of info to start with these are air core reactors and they are operating at 17kV and have a fault duty of 65KA.