Recent content by parlitu

  1. parlitu

    Equipment ground connection testing

    Does anyone now if there is any Standard, that required equipment grounding connection testing (resistance measurement) from equipment to the ground grid? Or a visual inspection is enough? I dont find any requirements in NFPa70. Not sure if resistance measurement from equipment (motor...
  2. parlitu

    Motor Space heater size and terminal box according to NEMA standards

    In NEMA 01 is specified that "For machines rated 601 V and higher, accessory leads shall terminate in a terminal box or boxes separate from the machine terminal housing. What about lower than 600V? Is a terminal box required by NEMA for space heater leads? Is there a table with space heater size...
  3. parlitu

    Splicing old electrical feeder to new

    Hope I understand the question. 1. I will not consider the conduit as a ground for the panel. The new panel has to have it own ground in my opinion. However article 344.60 says RMC shall be permitted as an equipment grounding conductor. 2. Each conduit has to be grounded. From this point of...
  4. parlitu

    Is there any standard to describe how long a commissioning test is valid?

    I start commissioning test for some switchgear 2 years ago. I did not finish commissioning, and due to company low budget, I had to stop this work for 2 years. Are those test that have been performed still valid? Or those test should be repeated again? Is any Standard that describe this? I will...
  5. parlitu

    MV Cable insulation testing

    As you all understood, I am interested in finding the best method on the market to evaluate expected life expectancy of cables. As I red into some papers on the internet, and also in a EPRI report, usualy they recommend tan delta that will give a average information about insulation (can't made...
  6. parlitu

    MV Cable insulation testing

    What testing method for MV cable insulation do you thing is more reliable? A tan delta that gives a general quality of insulation for entire cable plus a pd test? Or tan delta plus VLF hipot test? I am looking to find the best way to do cable insulation testing, and I need a method that can tell...
  7. parlitu

    No load current on a motor

    Usualy the no load current can get to 30% of nominal current. So 90A seams a little high; First step is to check the bearing health. One cause that can get to a higher current is if you just put vaseline to you bearings; in this case at the beginning the current will be a little high but if you...
  8. parlitu

    Overcurrent effect for motors

    Thank you all for response; One answer for Elmotor; it's S1 duty. We will try to mount a temperature sensor.
  9. parlitu

    Overcurrent effect for motors

    Isolation class - F. According to manufacturer, this motor can work to a temperature of 100C. The air flux is cooling down only external frame. Protection- IP55 according to IEC Publication 34-5 (but I don't think that counts). Also according to manufacturer, this motors can work with 108% from...
  10. parlitu

    Overcurrent effect for motors

    A motor of 45 kW from a ventilation unit, (nominal current 82A) due to a bigger load, function actually at 95A-measured current. The motor is cool down by a big air volume of 15C degrease. What are the odds that this motor to be burn? All the cold air can compensate the overcurrent effect? I...
  11. parlitu

    Different current values for motor pums

    13.5A each. The instalation is design to work with one pump in stand-by and only one pump running and we usualy do this way, but 2 weeks ago, bouth pumps where on, and I observe this diference between currents. Probably the current is bigger when bouth pumps are running due to a bigger pressure...
  12. parlitu

    Different current values for motor pums

    In one instalation of two identical centrifugal pumps that feed the same collector, I observe that if bouth pumps are running the current is around 13.5A, but if only one is running and the other one is in stand-by, the current is 11.8A. The nominal current of motor is 12.5A. Can someone explain...
  13. parlitu

    When thermal relay test fail

    Supose I test a thermal relay (bimetalic) using current injection-2*setting current(Is) and the tripping time is not correct. Let say is bigger. What will be the write action? 1. Adjust the setting current of thermal relay at a smaller value-Iss and inject again 2*setting current(Is). The...
  14. parlitu

    Merlin gerin masterpact problem

    First of all, you shoud install a current recorder (if you have one) on all three phase, and let it there until the breaker trip. You will find out the exactly current values (maybe there is a peak value, cause by a load starting, transformer, or motor, or something else) and you will be with...
  15. parlitu

    Thermographic scan

    Is there any prescription that say from what voltage or current thermographic scan is relevant? If not, from yours experience can you give some values? Thank you!