  1. opmgr1

    about constant current source

    Gentlemen please keep it civilized and professional. This is not the site to be posting insults!
  2. opmgr1

    Power transformer protection with distance relays

    There are some interesting discussions on inrush mitigation in thread238-235674. Why use distance relay as back up for transformer protection? Why not 50/51 and distance relays for your transmission lines?
  3. opmgr1

    Parallelling transformers during switching

    If you are matching tap position and not voltage, what happened when there are two transformers with different voltage per tap position? Theory indicated that greater level of circulating current will result from matching tap position than from matching turns ratio. I have heard of instances...
  4. opmgr1

    Parallelling transformers during switching

    The utility where I work do not match regulation (tap position) for the exact reason that you mention, there will be a voltage difference enough to result in a short circuit. Instead what we do is to match voltage which is a form of impedance matching. The fact that the turns ration are now...
  5. opmgr1

    arrester failures

    I would not pressure the utility too much on this, being a utility person myself you may find that you ran into a dead-end and there is no information from them to support the theory of an over-voltage. The fact of the matter is that based on the exposure of the lines, utility customers will be...
  6. opmgr1

    Resettings overloads after Capacitors installation.

    jraef's second post is more accurate. Step 3 of the first post is implying an algebraic subtraction, however these quantities are vector quantities and cannot be add algebraically!
  7. opmgr1

    Backfeed on 3P, Wye-Wye Padmount

    Waross, I am not sure I understand you post. With the neutral tied to earth how is it possible to have a neutral shift? Isnt the unequal voltage as a result of voltage drop along the lines and the neutral?
  8. opmgr1

    Backfeed on 3P, Wye-Wye Padmount

    This is an interesting one. For grounded wye- grounded wye system there will only be feedback if the transformer is loaded and the load is not balance L-G loads. There will be feedback for loads connecetd L-L especially motors. What is the nature of the load supplied by this transformer?
  9. opmgr1

    arrester failures

    For a station class arrester you may want to go with pressure relief of 80kA min. Look through the hubbell arrester catalogue for additional info.
  10. opmgr1

    Backfeed on 3P, Wye-Wye Padmount

    Is this a floating or grounded wye system?
  11. opmgr1

    arrester failures

    Yes, Voltage rating of the arrester. What type of damage(s) did the switch gear sustained? Anything from the utility regarding the EF?
  12. opmgr1

    arrester failures

    Nothing to be embarrassed about!
  13. opmgr1

    arrester failures

    These ungrounded systems are succeptable to ferroresonant over voltage, overvoltage (as much as 1.73pu rise) as a result of earth fault transient overvoltage, and overvoltage as a result of switching switching (whether deliberate or as a result of protection from faults). If there is upstream...
  14. opmgr1

    Network impedance

    Use the nominal ohmic/pu value for the network impedance. The voltage factor c which can be considered as a sort of safety factor should then be applied to compensate for Voltage variations, changing of the transformer taps etc. For the system you described (>35kV) the voltage factor c=1.10...
  15. opmgr1

    arrester failures

    Is this a wye or delta connected system?