Thank you for the feedback, I appreciate it. EnergyCAP is one of the ones that has been floating to the top of the list. It is good to see another recommendation for it from a different perspective than a university peer.
Import of the monthly data seems to be one of the common troubles with...
This is probably a bit of a stretch, given that it's a pretty niche area, but I thought I would ask and maybe find that someone does have a suggestion.
I work as an Engineer for a university in their energy services division that provides several utility services to campus, including steam and...
Here is an example of one of the phases showing the voltage and corresponding current. There does not appear to be any sort of voltage 'spike' precipitating the incident.
https://files.engineering.com/getfile.aspx?folder=1cea74ae-998c-4c9a-b4d5-b67647c25ec6&file=v1_i1_5_28_18.jpeg
We have an chiller / cooling tower installation that is using these new direct drive / permanent magnet motor application that requires a special VFD that runs at about 7Hz maximum speed. I do know that these were the first of this size in this application. We have three of these installed...
First, I would like to thank everyone for the replies.
This is a subject we've been down before with this installation, to which we're expanding the capacity. On each of the installations, we've done the IEEE519 modeling and it has said put the filters in but in reality, we've questioned their...
My state, North Carolina, will allow you to take the PE without the EIT / FE with 20 years or more of engineering related work experience, at least four of which must have been under the supervision of a PE. I am 3.5 years into the four year part and have roughly 19 years of work experience...
I have a question about an unusual installation. The current situation is as follows: 12.4KV utility service to a step down transformer that reduces the voltage to 4160V. The 4160 feeds a chiller VFD through a motor disconnect. We're looking at adding another variable speed chiller. One of...
Is your piping really designed as shown in the diagram in the initial post? This doesn't look like a primary secondary loop. It looks more like a variable primary (lack of bypass on the chiller output) without the VFDs on the buildings.
With constant flow / three way valves, you are undoubtedly going to have to make some form of trade off: efficiency, chiller cycles, or temperature and humidity control. In the worst case (and I've seen this happen in your situation is that you get a serious mold problem). About the only thing...
It has been my experience that a common indicator of this being about to happen is when middle managers are suddenly having a bunch of closed door meetings with each other.
Always remember that in every stage of the interview, they are looking for a reason to NOT hire you, not a reason to hire you. Many of these questions are opportunities to see if you will stick your foot in your mouth given a chance and your objective is to decline the opportunity.
As far as...
This is inline with the response I received from the Raleigh office rep, who also explained that the information isn't really available online either. The response is below. From the reply, If your willing to share your location, at least down to the nearby major metropolitan area, I can get...
DOH!, here is the link: http://www.training.carrier.com/commercial/hvac/general/0,,CLI1_DIV44_ETI12280,00.html
At closer look it also shows that it has a list of class locations and schedules. I have also contacted the local office to see if they have any recommendations.
Here is a link to a site about their training. It looks to me like a site where you can order the training modules. The course I took was held in Raleigh, NC and they brought a couple of guys down from Syracuse to teach parts of it. I will contact the person in charge of the course I took and...