Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by njengr1

  1. njengr1

    Cable residual voltage time constant

    ausphil Thanks for your input. At last someone got it. The phenomenon is the issue. I, like you, have been involved at the high end (>>138kV). Much of the SF6 filled buses and breakers and isolating switches at these levels have built in grounding and isolating switches. Sometimes with TV or...
  2. njengr1

    Cable residual voltage time constant

    burnt2x Your getting close to the point. from1910.296(n) "General." For the employee to work lines or equipment as deenergized, the lines or equipment shall be deenergized under the provisions of paragraph (m) of this section and shall be grounded as specified in paragraphs (n)(3) through (n)(9)...
  3. njengr1

    Cable residual voltage time constant

    Thank you for your opinions. I was really looking for some helpful experience. Note that OSHA and most industrial safety procedures don't require grounding LOAD circuits whenr the entire switchgear lineup has been deenergized, cleared, tagged, and locked out. If you have done some HV DC...
  4. njengr1

    Cable residual voltage time constant

    An electrician got a minor shock from a 4 kV EPR insulated cable after the cable was deenergized for 45 minutes. While the fellow wasn't hurt the safety folks are interested in establishing a procedure that will prevent this. Initially grounding the cable appears to have been done by momentary...
  5. njengr1

    Induction motor temporary coil repair

    We have a 15000 hp induction motor that has experienced a coil insulation breakdown due to system lightning surges. Can the coil be isolated from the phase winding and permit the motor to operate on a temporary basis? Any experience doing this would be appreciated. I expect there would be an...
  6. njengr1

    Need for generator breaker before step-up transformer

    Gents, The project that started this thread is a small cogen installation in a plastic fabrication plant. Two 2000 kVA gas engine driven units supplement utility power. It was built without the generator breakers. The question arose during a transfer of ownership. One engineer stated it was...
  7. njengr1

    Need for generator breaker before step-up transformer

    Your right about inspectors many of those I met didn't understand what an interrupting rating was on a molded case breaker. Previous NEC editions provided room for a professional engineer to make design decisions. Now the committees try to provide pre-engineered packages. We can at least be...
  8. njengr1

    Need for generator breaker before step-up transformer

    ScottyUK, Your practice is pretty much universal for the big units. jbartos, This system is a small generator (2MW) connected directly to the transformer. The transformer is a wye at 4.16kV and delta at 13.8kV. Both the wye point of the generator and the wye point of the transformer are...
  9. njengr1

    Circuit Breakers with different short circuit ratings

    uno, If you use U/L labled molded case breakers check out what the interrupting rating really means. The U/L test method calls for about 10 feet of wire on the load side of the breaker during the test. The wire used will be the maximum size permitted for the breaker size. On the smaller breakers...
  10. njengr1

    Need for generator breaker before step-up transformer

    rmw, Your right about the safety and lockout tagout, but the presence of a generator breaker really doesn't improve safety. Most units avoid generator breakers between the machine and the step-up xfmr because the price is high. The last unit I commissioned in NJ was 250MW and a generator breaker...
  11. njengr1

    Need for generator breaker before step-up transformer

    I think I found the answer to the need for a generator breaker. Art. 705.21 DISCONNECTING MEANS, EQUIPMENT on page 2001 of the 2002 NEC HANDBOOK describes the exact case I was investigating. If the generator and transformer are designed to operate as a "unit" no disconnecting means is required...
  12. njengr1

    Failure of Power Factor Correction Capacitors

    Having just finished investigating the destruction of a 21MVA bank operating at 27kV it is apparent caps are very sensitive to overvoltage. The stated max voltage for continuous duty is 110%, but no responsible vendor will sell a design rated to operate at the level. IEEE Standard 18 has a table...
  13. njengr1

    Area Classification

    As a former member of the API 500 /505 committee I can tell you these standards are based on keeping the oil business safe. The NEC has adopted these standards in 70A and other documents. If the Auhority Having Jurisdiction feels a particular site needs a hazardous classification, then the NEC...
  14. njengr1

    End of Life

    Anyone know of any reliability surveys that include dry power transformers in the 500kva to 2500 kva range. Specifically, the mean time to failure or life expectancy. Looking for 4160 to 13.8kV types
  15. njengr1

    Need for generator breaker before step-up transformer

    Thank you for the responses. The NEC is pretty quiet re generator installations. Re transformers, the NEC states nothing about step-up transformers. The table in the protection section 450.3(A) table doesn't require "secondary" protection for a "supervised location". The code is very vague on...