Pleae advise on the easiest connection cables and comms set up of the following.
Software is RS Logix 500 V5.20.00, RS Linx, PanelBuilder 32 V 3.80.00.
PC is old, runs on win ME with a 9pin RS232 port.
PLC is one year old Micrologix 1200.
I need to connect a AB 550T HMI to the PLC and also...
Thanks to all.
The reason I ask is that a couple of years ago I was involved in a scheme where the 11kv/433V Dyn11 Tx (No onboard isolator) was installed and the ACB was some 40-50m distance away. The DNO made us install a local ACB within 15m (cable length) of the Transformer LV terminal box. I...
Hi,
Can anyone tell me if there is a minimum allowable cable distance from the LV output terminals of a MV/LV transformer, say 1MVA, 11kV/433V to the CB, and what regulations/standards will apply in the UK.
Thankyou.
Old Relay.circa 1970's
Can anyone tell the time a Reyrolle 3B3 relay takes to trip.
The relay is set up as a REF. Instantaneous.
Set for 15V (0.5A) sec current from CT (1200/5)
30ohm resis in parallel with relay.
ie what is defined as "instantaneous" in this case, or is there a curve somewhere...
Hi,
An earlier thread (238-118313) shows a Generator withstand curve according to NEMA MG1-16.45
Is there an equivalent curve under IEC / BS / European standards, and if so could someone direct me to it or post it on this site.
Is there a minimum recommended time that standby low voltage (400V -...
Hi,
ScottyUK
Thanks for your response.
I have being back to site to check on a few things.
The type of panel view is 2711 - T5A5L-1, Ser B, Rev E, FRN 4.46 and powered by 24V dc.
The dc connections are correct.
The cable between the PV550 and the SLC 5/03 is a 2711 - NC13, which as far as I am...
Hi,
System
PLC -- SLC 5/03
HMI -- Panelview 550
Connected cables
From SLC 5/03 Serial Port to PV 550 Serial Port (RS232)
From PC Serial Port via 1747 PIC to SLC 5/03 DH485 port.
Software (old but usually works ok, have not had any problems before using it)
RSLogix 500 V5.20.00
Linx Lite...
Hi,
I am having some difficulty with the following, any input is gratefully received.
System
AB SLC 5/03.
1746 - HSCE Card for encoder 1024ppr encoder input.
1746 - N104V 2channel analogue input/output card.
Drive roller dia = 100mm (~4inch)
The encoder is mounted on the motor shaft.
The motor -...
Hi,
System
AB SLC 5/03.
1746 - HSCE Card for encoder 1024ppr encoder input.
1746 - N104V 2channel analogue input/output card.
Drive roller dia = 100mm (~4inch)
The machine drive roller pulls material through the machine at about 10m/min
I need to measure the speed of the machine via the encoder...
Thanks jde777,
I have looked at the info and it is pretty thorough.
However I am still unsure whether or not I need a seperate power supply for the encoder, or does it derive its' power from the 1746HSCE card.
Regards,
mrbj
Hi,
I have been asked to modify a machine as follows.
On site there is a SLC 5/02 plc (1996), with spare slots.
I am using RS logix 500 V5.20 software. I know its a bit old but it works.
I have been asked to add the 1746HSCE card and connect an AB 845 diff encoder.
This is to measure the...
Hi,
Installation approx 50years old.
Low voltage 230/400V.(UK).
0.5sq in (~300mm2)4core PILC cable.
Cables/Gland Boxes located inside switchroom.
Problem
The black pitch/compound that is used to 'pot' the end of the cable into the cable gland/termination box is leaching / leaking out, and...
Higuys,
I have an existing AB 5/02 plc on an existing machine.
I have been asked to modify the machine so that it can determine the position of a product coming down the line.
Currently this is done by a proxy detecting a stud on a gear wheel.
It needs to be more accurate.
I propose to insert a...
On low voltage systems, (UK 400V, 3ph+N ) and using Single core/Copper conductor/Aluminuim outer cables, 2per phase.
What is the standard practice for glanding off the Alum' armour ie..
a. Gland,terminate and bond both ends to earth, and use Al armour as earth return. or..
b. Gland, terminate...