  1. milwaukeebob

    120/240V 1P-3W, 100A Service to Very Remote Building

    Thanks dpc and waross. Always a pleasure to read all your responses to various questions/issues posted on eng-tips. You guys have made me a better engineer over the years. I agree with both of you that medium voltage would be the way to go but, as indicated, there are commercial issues...
  2. milwaukeebob

    120/240V 1P-3W, 100A Service to Very Remote Building

    Greetings everyone, I have a question regarding a fairly straightforward but odd situation/request that I've not seen in my plant days. The majority of my experience is in plant generation with fairly limited cable lengths and standard configurations. In short, I have a customer who needs...
  3. milwaukeebob

    Equipment BIL Rating Concerns

    Kiribanda, Thanks. These arresters were not selected be me. I will have to ask the EPC Contractor who is responsible for integrating this into the existing substation. This Contractor is also the original designer of the Substation. I will have to ask them the question. Unfortunately, I came...
  4. milwaukeebob

    Equipment BIL Rating Concerns

    Hello, I was recently brought into a project that involves installing a new piece of electrical equipment into an existing substation. The new equipment (a harmonic filter bank) is being installed on the 24.9kV of the substation. The substation is located at ~7150 feet above sea-level and...
  5. milwaukeebob

    NEC 110.26(C)(2) ...Egress from Working Space for Large Equipment "Rated" 1200 Amperes or

    Thanks dpc. I agree with your assessment. Unfortunately, there's no traditional AHJ on this very unique project. Regardless of the situation, if I had been responsible for the design, I would've put a second exit in the room on opposite sides of the gear regardless of the rating. Unfortunately...
  6. milwaukeebob

    NEC 110.26(C)(2) ...Egress from Working Space for Large Equipment "Rated" 1200 Amperes or

    I have a question related to NEC 110.26(C)(2) and an existing electrical MCC room installation. The installation has an MCC with a 1200AF main incoming circuit breaker (CB) that is set at 800AT. The MCC is labeled and rated 1200A but set to trip at 800A. The upstream CB feeding this MCC main...
  7. milwaukeebob

    Fire Pump Controller/ATS Normal versus Alternate Source Requirements

    Thanks waross and FacEngrPE. I know this will fly in the face of everything you know but there is NO traditional AHJ on this project. I understand...makes no sense but that is the reality. This is not a traditional utility or IPP building this small facility. Unfortunately, we currently have...
  8. milwaukeebob

    Tee connectors in Switchgear

    I've been in the industry for some time and the only application where I've personally seen these t-body connectors used are in xfmrs, but I know they can be used in switchgear. Your picture showing the t-body connectors suggests very limited space for the terminations. A traditional bolted...
  9. milwaukeebob

    Fire Pump Controller/ATS Normal versus Alternate Source Requirements

    I have a question regarding a fire pump/motor and associated fire pump controller/auto-transfer switch (ATS) installation at small power generation plant (<40MW). The plant is in the final stages of installation and commissioning has already begun. Note the owner of the plant is not a utility...
  10. milwaukeebob

    MV Switchgear Ground Bus Connections to Ground Grid

    Che12345 and Waross, thanks for your feedback. Understood. I've never seen only one (1) ground-grid riser connection to a MVSG bus in my 25+ years. Thus the reason for my question. One important point I need to make is that I'm coming into this project very late as an "observer". I in no way...
  11. milwaukeebob

    MV Switchgear Ground Bus Connections to Ground Grid

    Hello, Have a question about a line-up of medium voltage (MV) switchgear. This is one of longer line-up's of gear I've encountered in my career measuring almost 40' in length. The main bus is rated 15kV, 2000A, 25kA, 3PH-3W and consists of seven (7) feeder breakers from very small generators and...
  12. milwaukeebob

    NFPA Definition of &quot;Structure&quot; and Ruling

    Thanks cdafd. Understood. I need to take a deeper dive into NFPA 850. Yes - the building of a wall (or in this case extending one) would be the correct choice. Unfortunately, there's some challenges associated with that. Again, I appreciate all your feedback.
  13. milwaukeebob

    NFPA Definition of &quot;Structure&quot; and Ruling

    Thanks cdafd. Appreciate the feedback. Yes the project is in the U.S. Also, thanks for the link...I've seen this before. My question is ultimately related to NFPA 850 (Recommended Practice for Fire Protection for Electric Generating Plants…) Chapter 5 (General Plant Design) section 5.1.4...
  14. milwaukeebob

    NFPA Definition of &quot;Structure&quot; and Ruling

    Hello, I have a question regarding the NFPA definition of a structure. I know in the 2017 Code the definition of a "Structure" was changed. The definition now states "That which is built or constructed, other than equipment. (CMP-1)". They added the reference to equipment for clarity. I am...
  15. milwaukeebob

    Small Concrete Pads and Acceptable Levelness Tolerances

    Thanks Swinny. I don't have any experience with domed pads but I understand what you're saying and in many applications would be ideal. I whole-heartedly agree the much tighter tolerances you mentioned are very easy to achieve and 2.5" is unacceptable. I've seen alot in my 30 years in the...