Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by Mike Mike

  1. Mike Mike

    Shear Lag

    Thanks 217808, I had not seen this article before and have not dug into the canadian standard, but assuming x bar prime is the same as x bar this formula gives U = 0.43, plenty for our scenario. Packer's paper appears to be behind a paywall, but I did reach out to him directly. I agree if...
  2. Mike Mike

    Shear Lag

    217808, #1 The specification does not state the length of the weld must be greater than the width of the HSS. In my opinion the l >= H notation notes the limit of applicability of the simple formula. #2 How do you know AISC would say no? Do you know of anything they've said on this topic? #3a...
  3. Mike Mike

    Shear Lag

    Human, I agree and you are correct. Compressive buckling controls member design, LRFD capacity is only around 140k. We have always just specified the rule of thumb minimum weld length for this scenario but I'm questioning our decision for 2 reasons. One, I want to improve myself, so I'm digging...
  4. Mike Mike

    Shear Lag

    Thanks JAE, I spent a half hour unsuccessfully hunting for that reference. I found "Guide to Design Criteria for Bolted and Riveted Joints" Kulak, Fisher, and Struik 2nd edition 1987 and skimmed thru it, but found no reference to our discussion. This appears to be a discussion of research by...
  5. Mike Mike

    Shear Lag

    Hi all, what is the minimum weld length for tension members? We are designing a ton of welded knife plate connections for HSS10x10x1/4 tension and compression braces. The LRFD tensile capacity is 371k. The LRFD axial load is +-100k, so we only need (4) 6" long 3/16" fillet welds, and we only...
  6. Mike Mike

    Do these deck beams look stable to you?

    phameng, I still didn't have time to dig into your links yet (doing real work over here), but came across another dropped beam. this one is probably fine right?
  7. Mike Mike

    What are the limits of prescriptive design?

    lex, Great find on the repeal of the 2006 wall anchorage requirements. Here's a screenshot of the 2006 code: 5" OC!!! quite a difference from 6', no wonder the powers that represent the contractors flipped, here's the movement to squash it: I have no issue with their conclusions. If they have...
  8. Mike Mike

    What are the limits of prescriptive design?

    lex, I can't find any Gnijolli on google, can you send a specific reference? I forgot about R602.3 and after re-reading it I agree with XR's interpretation: "studs shall be continuous ... to... foundation... floor, ceiling or roof diaphragm". I think you and XR are saying the same thing. XR was...
  9. Mike Mike

    What are the limits of prescriptive design?

    lex the photos are from your link Florida disaster preparation hurricane retrofit materials, maybe I clicked something on the site lol. the article explains that you are correct in that the most common failure is in photo 1: the roof ripped off the top of the gable wall and the issue here has...
  10. Mike Mike

    Do these deck beams look stable to you?

    gte and lex, I agree and have typically been requiring simpson ACH caps at a minimum. I just talked to a deck inspector with the county with decades of experience and he said he does require contractors to add bracing for these situations. he said he tells contractors that cap manufacturer...
  11. Mike Mike

    What are the limits of prescriptive design?

    lex great link as usual, basically telling homeowners that yes politicians and special interests screwed you over yet again, sorry maybe I'm too cynical I should reserve judgement. But the way this reads to me is here's a list of shitty things that are going to happen to you and could have been...
  12. Mike Mike

    What are the limits of prescriptive design?

    lex you are correct IRC does require complete load paths, but I'm not sure how it expects non-engineer IRC users to trace loads. I just spent another hour reading thru this and the wood portion is completely silent on ceiling diaphragms, but the cold form portion gives the following guidance...
  13. Mike Mike

    What are the limits of prescriptive design?

    great points lex on adjusting safety factors for the specific limit state and differentiating between life-safety and performance. funny how we use the same handrail safety factors whether it protects against a drop of 1 ft or 1000 ft. RWW, you mentioned the gable wall hinge and it got me to...
  14. Mike Mike

    What are the limits of prescriptive design?

    lex, thanks for the links. I'd like to focus on the ICC committees rather than the local committees. I assume joining the ICC committees is unpaid volunteer effort. I do see ICC is looking for a new CEO and "Government Relations and Operations Associate" on their website, which would certainly...
  15. Mike Mike

    What are the limits of prescriptive design?

    RWW I ran a quick engineering check on three 20' tall 2x6 stud grade kings at the side of a 14' wide opening for 129mph, exp C, 35psf unfactored C&C wind load, 300% overstressed in bending, 5" deflection. Hopefully the homeowner doesn't mind his walls shaking and drywall cracking. no no it's...