Heat load from each device is found in the device's data sheet.
Positive pressure will keep dust away but will consume more energy.
Filter type depends on the application requirements: MCC may be NEMA 1, 4, 14 etc, and may provide the required protection.
For high loads such as VSD, it is best...
I implemented the idea described in iOmega's reply in several projects some years ago (VFD digital input to triger preset speed, and turn on the catching circuit.
Rule of thumb for fans:
Power ratio is the cube of speed ratio, flow ratio is the speed ratio, pressure ratio is the square of speed...
To Macbeth
I have to disagree with your theory.
Lower DT means constant "capacity" with increased GPM across the coil. Actually you refer to constant prevailing "load" and not to increased potential "capacity".
With DESIGN heat load and increased GPM (beyond design...
Water coil Heat transfer coefficient increases with water flow.
Heat transfer rate (water to air) is directly proportional to the product of water flow rate and water temp rise through water coil.
This means the AHU water coil has a larger capacity with increased water flow rate.
I use an household dryer with embedded air-air HX.
The heated (secondary) air has no odor and has very low humidity. The primary humid hot air is cooled by the ambient secondary air, and the condensate water (from the primary hot humid air) is piped to the drain.
The additional required power is...
The answer is no, and this is why:
Increased coil area and increased airflow, assuming coil temp does not increase, means more Btu/hr absoarbed from the conditioned space. To handle this, the condensing unit will have to increase condensing temp, lowering compressor capacity, when actually...
I failed to mention an important aspect:
The regeneration system is connected to mains power lines to supply the network when regenerating.
If mains supply disappears for any reason, you will have NO BRAKING!!! You will need powerfull emergency braking/holding drum to kick in on mains failure.
I suggest using a VSD in conjunction with an embedded/external regenerative breaking system.
This may not be the cheapest to install, but I believe will have the lowest overall price (design, install, maintain, control, operate).
Such a unit works in a cement factory for several years now...
Temp control (not on/off I presume) is optimized at full airflow capacity, therefore it is recommended not to very it. This means negative pressure control via exhaust control.
Door undercut or grille is acceptable if the infiltration air quality is not important.
Use HEPA filters on exhaust if...
I want to add some observations, based on the assumptions the calculated heat load is 30,000 Btu/hr and the calculated airflow is 1450 cfm:
Thumb rule figures:
400 cfm/Tr: yours is 1450/2.5=580 (+45%)
350-700 sq ft/TR: yours 3300/2.5=1250 (>+78%).
030 evaporator at 67F WB RA and 40F evaporator...