  1. mayanees

    15 kV EPR cable 3 or 5 mil tape shield?

    Dear forum folks, We're doing a project where 15 kV EPR with a 5-mil tape shield was specified. A vendor has submitted that cable with a 3-mil tape shield. Does anyone have any experience with the 3-mil wrap cable to suggest we stay away from it? Any opinions and recommendations are...
  2. mayanees

    Square D Power-Style fusible Switchboard

    Thanks dpc for the reply. Yes the Utility contribution is suspect at 200kA. However, what they've shown me certainly has the potential. There are (5) 40kA sources in a spot-network located 20 feet from the gear. The Utility (Con-Ed) reports 200kA for the 480 and 208 Volt sources, as in 200,000...
  3. mayanees

    Square D Power-Style fusible Switchboard

    I'm working on a system that was originally installed in the late 60s or early 70s that has two 208V, 4000-amp Square D Power-Style switchboards with fused bolt-loc pressure switches (FBPS) as the service entrance devices. The gear is labeled: SUPPLY BUS BRACING 100kA on one piece of gear, and...
  4. mayanees

    Emergency Power System - mode of operation

    Thanks for the reply David. That's my thinking as well, but having 40 years of satisfactory performance, I think they'll be reluctant to change. .. unless I can make a strong case for it.
  5. mayanees

    Change Settings on Protective Relays

    You've raised a couple points that warrant discussion. First and formeost, if you found a neutral/ground problem, then the Study's settings may have been appropriate, and not warrant changing. And as an earleir post states, one you change it, you own it. But gf settings can be subjective. Many...
  6. mayanees

    Emergency Power System - mode of operation

    We are developing a design for the upgrade of a 40 year-old, 13.8 kV Emergency Power System. The existing system consists of two (2) 3.25 MW, 13.8 kV diesel gensets. These sets energize fourteen (14) 13.8:0.48 kV substations throughout a campus-wide system. Genset operation is initiated by...
  7. mayanees

    Medium Voltage Air Circuit Breaker upgraded to Vacuum

    I just talked to him and he will get to this board later this afternoon. He is cbsnuclear. John M
  8. mayanees

    Capacitor bank

    Your first choice, or the "low hanging fruit", will be larger AC across-the-line (atl) started motors with 0.8 power factor. Beyond that, the addition of pf correction caps in any electrical system needs to pay attention to harmonics that could cause problems. And I shouldn't even make the...
  9. mayanees

    ground current pick-up - CBCT for 3 phase motor

    I'd go with 20% of the phase pickup. John M
  10. mayanees

    Giants-Cowboys power outage

    I can tell you why, based on the limited information provided. The ground-fault trip was set to minimum. $1.6 billion spent on the stadium, but the Power Study was value-engineered out of the project, saving them $5-10 grand! Safe bet? John M
  11. mayanees

    Combined Transformer Inrush

    I'm coordinating an electrical system where a 1600 amp breaker controls six (6) K-rated dry-type transformers. To simplify the problem, I'll say they are all 150 kVA. The full-load amperage on a 150 kVA xf at 480 Volts ~ 180 amps. The inrush for a K-13 transformer can be as much as 15X. Using a...
  12. mayanees

    Do you actually carry around your PE pocket ID card?

    Two comments: 1) I'm on the DE PE Law and Ethics Committee, and we would never discipline someone for not carrying a crad - if it's even listed anywhere as a requirement. As noted earlier, online registration verification outdates card carrying. 2) I just ordered a DC PE rubber stamp, and to...
  13. mayanees

    starting a business

    Don't forget about Professional Liability Insurance. I used to practice as a two-man engineering shop with a hefty policy as required by one of my clients, for $3,000/year. In the 10+ years that it was active, I never had any claims. And when I stopped the business, the insurance company wanted...
  14. mayanees

    Work / Life Balance

    Smell the roses young man... My recommended steps for you: 1) Embrace the basement, because it'll never again be that simple. Fix it up. Get a pool table, etc. 2) Get into martial arts for fitness and self-confidence. 3) Get a hobby - for me it's old cars. 4) Learn to cook so you can eat the...
  15. mayanees

    Is there any reason to oversize power cables to motors?

    To David's point, absolutely, and thanks for that clarification. If that switchgear had 50 kA of available fault current, and 25 feet of #2 AWG cable is terminated on a 100 amp breaker, the fault current is reduced to about 30 kA at the termination of the cable. John M