Have a look at the following:
http://www.tew.co.uk/index.php?option=com_content&task=view&id=18&Itemid=83
for the UK
or
http://www.tew-eng.de/index.php?option=com_content&task=view&id=18&Itemid=83
for Germany
I have no connection with the company apart from using them for a quotation to...
Thanks Warpspeed, that makes good sense.
Olavurthomsen, It sounds an interesting problem you have there! I can well imagine it hapenning, but not sure of a cure. Maybe a large resistive load connected at switch-on and then turned off via a timer would absorb the transients, or MOV's connected...
I am aware of the potential problems of using long cables on the output of VFDs with the IGBT output switching causing a high voltage standing wave, stressing cable and motor insulation. Also problems caused by common mode noise from such systems.
Are the same problems likely with...
Crouzet are a long established company that do a good range.http://files.engineering.com/getfile.aspx?folder=6be0c46a-44a2-4714-bb85-76ed20f88388&file=Crouzet.pdf
When I was involved with electric furnaces years ago, we fitted flow switches in the water return pipes from each electrode. When the flow rate dropped below a predetermined level, it signalled an alarm. Simple and effective.
Some VFDs do not like driving into an open circuit. You need to talk to specific vendors if their drive is suitable or not.
My preference is to put the contactor at the input to the VFD and an interlocked isolator adjacent to the motor.
Thanks Scotty,
I was thinking more of the dip on the switchboards affecting other equipment when using a weak supply such as a generator. Contactor mfrs often quote figures of acceptable control voltage before they drop out.
Voltage dips can cause re-strikes on sodium lighting etc.
I was...
When doing calculations for voltage drop when motor starting, I have always used figures of 20% at motor terminals or 15% at the switchboards as maximum allowable.
Can anyone tell me if there is a British Standard that actually defines the allowable voltage drop and time periods when motor...
Thank you Keith.
I did notice that the OP wanted a symbol for a SLD, in which case my spider would lose another 7 legs! I vaguely remember borrowing this symbol from one of the motor manufactures literature.
I have been in the electrical Engineering game for over 25 years and spent 7 at...
This is what I use. Not sure where it originated from.http://files.engineering.com/getfile.aspx?folder=133beb3d-008a-45c8-b736-556e770c2e01&file=motor.pdf
Stuart,
I think this is the Siemens book that ScottyUK is referring to. I have found it to have some very useful references in there, despite its bias to Siemens products.
http://support.automation.siemens.com/WW/view/en/28813929
ScottyUK,
Didn’t Enron become NEL, then Carron Engineering...
For the jobs that I have been involved in at refineries, the storage tanks have always had separate earth pits / rods, the number of which depended on the size of the tank. Not connected to the main earth grid. I’m not sure of the reasoning behind this, just an observation I have made. I’m...
I have also used P&V, but as with all these database systems, you have to be diciplined in the way you name things. Uper case, lower case, full stops etc. It can be easier for the user to add a new part number than it is to search for an existing item.
Restricting users from creating new...