    connecting single phase to three phase delta heaters

    Thanks All, Here is an attachment from HEATCRAFT who makes the units. They use 4 defrost heaters and can arrange them for 230v/1p or 230v/3p or 460v/1p. http://files.engineering.com/getfile.aspx?folder=39597903-cc4f-4609-9e29-54a1f34a4897&file=LSF200_wiring.pdf
  2. lippy

    connecting single phase to three phase delta heaters

    Controls are seperate thru ssr and contactors. But I did find out there are in fact 4 seperate heaters in a delta configuration for 3phase 230V heat. How in the heck is that done? Does this mean that not all the heaters are the same? Thanks, your humble student of reason....Joe.
  3. lippy

    connecting single phase to three phase delta heaters

    Hello rcwilson, Thanks for the explanation. I get it. I will reconfigure as 3 heaters in parrellel at a total amperage of 19.6 since this is what I originally planned for anyhow. The two outta three idea without re-terminating the three heater leads is not the way to go but I do appreciate...
  4. lippy

    connecting single phase to three phase delta heaters

    Hello, I'm in need of electrical help as I'm a Mechanical Engineer who knows enough electrical to be dangerous....if you know what I mean. I have electrical distribution all set up for 230V 1 phase power to be delivered to resistive defrost heaters. The equipment unfortunately is designed as 3...
  5. lippy

    Low ambient conditions for RACCU

    Our refrig systems are probably considered a little non-traditional. I am well aware of how the Alco HP valve works. The modulating hot-gas valve, not the Alco HP, is a motorized (Siemens SDR-3) and controlled from a little PLC (0-10vdc) with a room temp set point. We use a lot of hot-gas...
  6. lippy

    Low ambient conditions for RACCU

    Thanks for responding. I have both an Alco HP8 with 110 psi condensing pressure set point and a seperate modulating hot gas valve on a hot gas line from the compressor outlet to the distributor side port on the dx coil. Is it possible that for 134-a I should have higher setpoint specified...
  7. lippy

    Low ambient conditions for RACCU

    Hello my fellow engineers, Here is my problem. I have a small Copeland RACCU, R-134, 3HP. It is used to cool a dry room with a Munters dryer. We use hot gas bypass into the dx coil in the room for modulation and heat because the room is to run at 77F. Well, I can't get enough hot gas to...
  8. lippy

    Perforated Ceiling Air Distribution System

    Hello, I too get into perfed ceilings in small(100-300) sq.ft. controlled temp. (CT) rooms. SMACA's HVAC System Duct Design has a table 14-17 on page 14.48 that gets into a a coefficient factor for doing calculations regarding pressure drop and air flow. We use Hunter-Douglas steel perf panels...
  9. lippy

    Pressure drop from perforated ceiling panels.

    Thanks fellas. The discussion is good for me too. I am in process of requesting that $124 SMACNA Duct Design Book for the library. Cheers.
  10. lippy

    Pressure drop from perforated ceiling panels.

    I know there are other losses assoc. with the air circuit (ie: blowers, refrig coil, duct bends, intakes). I am just concerned with calcualting what would be the pressure drop thru a perf. pattern as a function of %open area. You see the volume above this perf. panel is essentially the volume...
  11. lippy

    Pressure drop from perforated ceiling panels.

    What about the the "K" factor for perforated plate like is found in this following link? http://www.inres.com/Downloads/HVAC_RR.pdf Here is the real life situation I am dealing with: I have to blower modules facing each other in a room 11'deep by 7'wide. They blow 1800 cfm each (0"SP blower...
  12. lippy

    Prehistoric HVAC engineers

    hELLO, I too am a relatively new ME to AEC/MEP but have been an engineer for 15 years. I do agree with you and have experienced "shock" at energy waste for indoor air quality. I see that LEED's and "Green Building" philosophy is addressing this somewhat. I think we need energy "hawks" on big...
  13. lippy

    Pressure drop from perforated ceiling panels.

    Accystan, Your assumptions of the problem are correct. I am glad you mentioned the "k" factor which is crucial when dealing with orifice obstructions in fluid flow. I will check if manufacturer of perf-ceiling panels (HunterDouglas) has such info. I, like yourself, wonder then if (K x...
  14. lippy

    Pressure drop from perforated ceiling panels.

    Hello, Here is the problem and what I think could be the solution based on the Bernoulli equation, but it seems too simple to be true. We have say 1000 cfm(@0"sp) being delivered to a ceiling plenum of 10ft x 10 ft. with .50" holes spaced every 4". That means I have 900 .50" holes giving me a...
  15. lippy

    DRY EVAPORATOR RATING CONVENTION

    Hello fellow knowledge seekers, We make custom hvac/refrig. system dedicated for particular close tolerance lab conditions. We match a ceiling mounted evaporator to the room load and to a Copeland condensing unit that has compressor, condensor, receiver pre-assembled. The evaporator coil manuf...