Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by LicensedToPEe

  1. LicensedToPEe

    Partition Load LL reduction - finally clarified (IBC 2024)

    Numerous discussions in thread507-438708 and thread507-161349 on this topic, initiated with IBC 2000/2003, well, a quarter century later and ICC has finally made a statement on this in IBC 2024. 1607.5 Partition loads. In office buildings and in other buildings where partition locations are...
  2. LicensedToPEe

    Historic rebar detailing 1B 1S

    @kipfoot: Are we then accepting that the would be only be a single top bar? Hasn't there been a consensus that there should be at least 2 bottom bars and 2 top bars (at supports) to keep the stirrups anchored as well as some idea of nominal continuity reinforcement? Based on the sections...
  3. LicensedToPEe

    Historic rebar detailing 1B 1S

    Working on a project from 1925, concrete frame building constructed by the War Department Quartermaster Corps Construction Services at Ft Benning, GA. The 1925 concrete details use the truss (bent) bars (round in section) in conjunction with straight bars (square in section). Q1: For a...
  4. LicensedToPEe

    Pre-Engineered Metal Building Roof Rod Bracing

    This is the door truss at a hangar with a fabric/curtain (or rigid, doesn't matter) door. Because of the large lateral load, a single bent frame (or truss) will not work. One typically ties the first two gravity elements (bents, trusses, etc.) together to create a box header truss/bent. Also...
  5. LicensedToPEe

    Seismic sway bracing and branch line restraints in SDC A & B per NFPA 13 (2013)

    Stookeyfpe, I think you're starting to see where I am coming from as a structural engineer. I too am inclined to say SDC A & B does not need seismic bracing. But so far in this discussion I don't see a clear statement of interpretation in IBC (and by reference to ASCE 7 and NFPA 13) that...
  6. LicensedToPEe

    Seismic sway bracing and branch line restraints in SDC A & B per NFPA 13 (2013)

    stookeyfpe I agree, ASCE 7 is referenced by IBC and it becomes "legal" by this means. However, ASCE 7 alone does not have legal merit. But I don't want to diverge from the original thread. My question remains: If IBC Section 903.3.1.1 states: "Where the provisions of this code require that a...
  7. LicensedToPEe

    Seismic sway bracing and branch line restraints in SDC A & B per NFPA 13 (2013)

    prinklerDesigner2, I believe there are other threads on this. There are no Seismic Category maps, only USGS ground motion parameters for 0.2 sec and 1.0 sec spectral response acceleration values in Ch22 of ASCE 7-10. With this information AND additional parameters (risk occupancy/risk category...
  8. LicensedToPEe

    Seismic sway bracing and branch line restraints in SDC A & B per NFPA 13 (2013)

    wannabeSE, the interpretation is somewhat vague in ASCE 7-10 exemptions. It surely does not say all mech & elect components. However more importantly, ASCE is a engineering guideline, not a legal document or "Code" like IBC is. IBC 2012 requires NFPA 13 compliance for sprinklers, and NFPA 13...
  9. LicensedToPEe

    Seismic sway bracing and branch line restraints in SDC A & B per NFPA 13 (2013)

    thread184-335672 I wanted to get back to this old thread now that it is 2016, 3 yrs after NFPA 13 (2013 print) has been out. I'm a licensed structural engineer (SE) working with a fire protection engineer (PE) in a project located in TX (that's actually irrelevant) in Seismic Design Category...
  10. LicensedToPEe

    Center Mass to Rigidity Eccentricity

    When it comes to modeling the structure using semi-rigid diaphragms, does the eccentricity value make a difference? Since the floor diaphragm is sub-meshed into plates (given it’s modeled as semi-rigid), the seismic and/or wind forces are NOT applied to the center of mass (as is the case of the...
  11. LicensedToPEe

    Historic Concrete Reinforcement cca. 1908

    SlideRuleEra, I’ve gotten papers from you before and again, you come thru. Thanks! The paper is a keeper…
  12. LicensedToPEe

    Historic Concrete Reinforcement cca. 1908

    I will be making some "lower bound" estimates on the amount of steel. I've looked in some old literature and woodman88 is right, there are too many patented systems. I'm taking a 3-1/2" x 3/8" plate as my "As" and ignoring the vertical 3" x 3/8" 'T' portion, to be conservative. Thanks, all!
  13. LicensedToPEe

    Historic Concrete Reinforcement cca. 1908

    Msquared48, Do you mind sharing as to how you calculate the 3/8" plate? What dimensions are you using to arrive at this thickness. I am not following based on your justification given above... Thanks,
  14. LicensedToPEe

    Historic Concrete Reinforcement cca. 1908

    I’m working on a building constructed in 1908 (the historic Univ. of Chicago campus) and I have encountered a strangely called out rebar in the floor concrete T-sections: 3-1/2”x3”x7.8# T bar. (Graphically shown as a rectangular plate.) Does anyone have any idea how to figure out the actual...