Recent content by Kiribanda

  1. Kiribanda

    Offshore power transformer YNd1 vs YNd11

    Looking into the SLD followings are my findings. 1) I have seen that in NORTH AMERICA the winding configuration is always Dyn1 whereas in the other side of the world following IEC standards the winding is mostly Dyn11. A solid reason is not known yet to me. The change can be made by reversing...
  2. Kiribanda

    Fault Current Analysis

    What is the MVA rating of the Yndyn transformer directly connected to the Utility bus?
  3. Kiribanda

    "Zero offset" in tranformer's inrush current

    Herivelto, The non-zero happens due to high DC off set meaning very high X/R ratio. Depending on the transformer design meaning its X/R ratio, it may happen. If we are going to break the current during the short in-rush duration, then the non-existence of current zeros may be a problem for the...
  4. Kiribanda

    Short Circuit Calculation - Impedance Method - Three Winding Power Transformer

    Why you need to calculate? It is very strange to know why you cannot find the name plate of such a large critical transformer operating at 400kV?
  5. Kiribanda

    CONNECTING PE TO CLEAN EARTHSYSTEM

    CLEAN EARTH was an old idea when the manufacturers were not able to explain some erratic behavior of process control units. It is no longer valid now. Bond them together to make an equipotential. Also by separating them 5m in the soli do you think that it is possible to stop influencing the other?
  6. Kiribanda

    Overvoltage During Earth Fault

    I have no further comments until I see the transformer connections (vector group) at the other end of all feeders H01 to H06 feeders which I have already requested from newelecteng by my post on 28 Sep
  7. Kiribanda

    PT ratings on impedance grounded systems

    1)Yes, you are correct. It is 2400V to ground. Therefore, no questions. You cannot use a 2400/4160Y PT on an impedance grounded system. Instead you have to use DUAL bushing, 5kV class, indoor or outdoor with a VTR=35 if your secondary system is 120V AC. Therefore, rated primary accuracy...
  8. Kiribanda

    Overvoltage During Earth Fault

    beyond86 Yes, but does it mean that the 33kV system has got 643A as charging current? How do you account for that? Before I make any further comments I am curious to know, 1) Is the 33kV system a real "DELTA" system? 2) Does the 33kV system really needs an earthing transformer? 3) If yes, how...
  9. Kiribanda

    Overvoltage During Earth Fault

    beyond86, Yes I noted it. See the feeder relay results. Io_calc =643.458(A) meaning 3I0=1929Amps is the earth fault current. How do you justify that amount of large earth fault current if the 33kV side is DELTA? If the 33kV system is really a DELTA bus then there is only the charging current...
  10. Kiribanda

    Overvoltage During Earth Fault

    newelecteng: I noted the following. From the incomer relay, I Found that U0=14407.808(V)=14.4kV Per your SLD the incomer is solidly grounded. Therefore,U0 cannot be 14.4kV. It should read 76kV. Per SLD there is no VT at the 132kV side. Any comments?
  11. Kiribanda

    Neutral/Ground Current When Closing Substation Tie and Downstream Tie

    keeverw, Could you please upload the single line diagram? It should show the impedance data of the transformers.
  12. Kiribanda

    Overvoltage During Earth Fault

    newelecteng: Few questions to you please. 1)What is the reason for using WYE EARTHED transformer for the 132kV side? 2)Are all feeders H01 to H06 connected to generators exporting power to 132kV side or are they normal feeders connected to typical loads? 3)What is the vector group of the...
  13. Kiribanda

    Overvoltage During Earth Fault

    1) What is the earthing method of your 33kV system? 2) You have mentioned that an earthing transformer ZNyn1 is feeding your 400V system. Bit unusual for me. Could you please upload your SLD?
  14. Kiribanda

    Grounding Transformer In distributed wind generation

    1) You are correct. The existing grounding transformer is directly connected to the existing 12.47kV distribution system. Per the given SLD, currently, the existing 12.47kV distribution system is ALREADY effectively grounded (Utility will not tolerate non-effectively grounded systems) and...