Dear All;
I am supervising 2 sites within one factory.
Site A:
There are 5 compressors running with ABB inverters. The inverters have modbus RTU built-in. They are monitored and controlled by HC900 via modbus RTU communication.
Site B:
There are 2 compressors (stand-by) operating with Danfoss...
GGOSS;
Thanks for sharing. To be precise, does it mean that the pump should stop under the same flowrate, suction pressure, and discharge pressure? (of course with 'certain' amount of tolerance).
I hope you don't have to shoot me for answering this one.....:)
Keith
Marke;
Yes, we used analog one that time to prove it to the motor vendor.
May be that is also the reason why it keeps showing RAMPING instead of RUNNING
Keith
Hi Marke;
You got it wrong. I make use the motorized valve AGAIN after all the failure to get soft stop. When I test-com, all the valves are let open.
The reason I shut the valve first is to rest the check valve so that there will be no shut slam noise. To customer, no noise means no water...
Ozmosis;
Thanks.
I always do AMA at least once when I test-com an inverter. But after that I do not do it anymore unless I press manual-initialization to return to factory setting
Edison123;
The vendor who supplied the motor came in and notice that his men did not do perfect aligning. So they...
Hi All;
Thanks for the advice. The problem solved. It turned out that the motor-pump coupling is not properly installed.
Hmm....then this must be a good feature of Danfoss inverter.
Keith
Hi Jraef;
Thanks for the input.
I forgot to inform you that in my proposal, I told the customer that the motorized valve will no longer be needed. And during test-com, we let the valves open all the time.
At the moment, I still make use of the valve. I close the valve first before stopping...
Hi Jraef and Ozmosis;
The application is for distribution pumps with 3 pumps (@ 75kW). Each discharge line has a motorized valve and check valve.
The pumps were run by star-delta starters in the past that is why they need the motorized valves.
So this is a retrofit project.
Two pumps are...