Recent content by Keith1976

  1. Keith1976

    Honeywell HC900 and ML50

    Dear All; I am supervising 2 sites within one factory. Site A: There are 5 compressors running with ABB inverters. The inverters have modbus RTU built-in. They are monitored and controlled by HC900 via modbus RTU communication. Site B: There are 2 compressors (stand-by) operating with Danfoss...
  2. Keith1976

    Danfoss softstarter MCD500

    Marke; Can I replace "similar external hydraulic effects" with "similar suction & discharge pressure"? Keith
  3. Keith1976

    Danfoss softstarter MCD500

    GGOSS; Thanks for sharing. To be precise, does it mean that the pump should stop under the same flowrate, suction pressure, and discharge pressure? (of course with 'certain' amount of tolerance). I hope you don't have to shoot me for answering this one.....:) Keith
  4. Keith1976

    Danfoss softstarter MCD500

    Hi GGOSS Could you please tell me more about your experience? What system did you face? What kind of inconsistency? Thanks in advance. Keith
  5. Keith1976

    Danfoss softstarter MCD500

    Marke; Yup...agree Keith
  6. Keith1976

    Danfoss softstarter MCD500

    Hi Bill; how to ramp the speed down "nicely" until the check valve closes? Its a softstarter. I dont get you. keith
  7. Keith1976

    Danfoss FC202 can not reach 50Hz output

    Marke; Yes, we used analog one that time to prove it to the motor vendor. May be that is also the reason why it keeps showing RAMPING instead of RUNNING Keith
  8. Keith1976

    Danfoss softstarter MCD500

    Hi Marke; You got it wrong. I make use the motorized valve AGAIN after all the failure to get soft stop. When I test-com, all the valves are let open. The reason I shut the valve first is to rest the check valve so that there will be no shut slam noise. To customer, no noise means no water...
  9. Keith1976

    Danfoss FC202 can not reach 50Hz output

    Ozmosis; Thanks. I always do AMA at least once when I test-com an inverter. But after that I do not do it anymore unless I press manual-initialization to return to factory setting Edison123; The vendor who supplied the motor came in and notice that his men did not do perfect aligning. So they...
  10. Keith1976

    Danfoss FC202 can not reach 50Hz output

    Hi All; Thanks for the advice. The problem solved. It turned out that the motor-pump coupling is not properly installed. Hmm....then this must be a good feature of Danfoss inverter. Keith
  11. Keith1976

    Danfoss softstarter MCD500

    Hi Jraef; Thanks for the input. I forgot to inform you that in my proposal, I told the customer that the motorized valve will no longer be needed. And during test-com, we let the valves open all the time. At the moment, I still make use of the valve. I close the valve first before stopping...
  12. Keith1976

    Danfoss softstarter MCD500

    Hi Jraef and Ozmosis; The application is for distribution pumps with 3 pumps (@ 75kW). Each discharge line has a motorized valve and check valve. The pumps were run by star-delta starters in the past that is why they need the motorized valves. So this is a retrofit project. Two pumps are...
  13. Keith1976

    Danfoss softstarter MCD500

    Hi All; Does anyone have experience using the above softstarter? The marketing article said that it has learning capability to have smooth stop. Keith
  14. Keith1976

    Danfoss FC202 can not reach 50Hz output

    Itsmoked; I reset the inverter to factory setting already. Then enter the "principle" setting only, i.e. motor data. Keith