For looped standpipes within the fire department pumping capability, is the standpipe hydraulic calculation allowed to take into account the loop design configuration to reduce friction loss in the system? If so, is it stated anywhere in NFPA 14 (2024 or earlier versions) to support this argument?
Both the ESFR and QR sprinklers are off the same zone (same compartment as well).
If the density/area calculation method for the QR sprinklers captures both QR and ESFR sprinklers, then flow both simultaneously?
A compartment contains both QR standard coverage sprinklers and ESFR sprinklers. The QR standard coverage sprinklers protect a mezzanine that is not separated from the adjacent warehouse protected by ESFR sprinklers.
For the hydraulic calculation at the boundary condition (where ESFR and...
[NFPA 13 (2013)] A combustible concealed spaced is created by fastening drywall tight to the bottom of a wood truss system. The wood truss has less than a 6-inch gap between the top of bottom chord and bottom of top chord.
Are sprinklers required within this combustible concealed space, or...
Are sprinklers required?
NFPA 13 (2013), sentence 8.15.7.1 states that "sprinklers shall be installed under exterior projections exceeding 4-ft in width."
Note that NFPA 13 does not consider private balconies to contain storage. NFPA 13 notes "the committee has stated that combustibles...
Assume this is ordinary hazard occupancy, 130 SF coverage.
The question is: based on the two scenarios in the link, is the scenario with the wall removed acceptable?
Good day,
All scenarios shown in NFPA 13 for design area are of single, rectangular, rooms. What about oddly shaped rooms? Take for instance Figure A in the attached PDF. Would each sprinkler cover 120 sq.ft. (15 ft. x 8 ft.), or would it be 172.5 sq. ft. (15 ft. x 11.5 ft.)?
Exhibit 8.7 of...
LCREP - NFPA 13R seems to be silent on sprinkler inclusions or exclusions outside of the building. Is this because sprinklers are not required or because we are supposed to use NFPA 13 for such areas? For example, in NFPA 13R are we supposed to protect combustible exterior projections greater...