  1. Gianoli

    GCB in the 15,000 Amp range

    They are all SF6 nowadays. Here is a link to one company's offerings: https://www.hitachienergy.com/ca/en/products-and-solutions/generator-circuit-breakers It used to be the domain of Airbast 50 years ago. There are still some around in service today.
  2. Gianoli

    6.9 kV or 13.8 kV to feed big synchronous motors?

    13,800 Pros: - 50% reduction in line current - May allow for simpler feeder circuit configuration due to lower currents. 13.800 Cons - Depending on the operating environment, - motor insulation systems will be more complex and potentially less reliable especially if the operating environment is...
  3. Gianoli

    Understanding Transmission System Power Flow

    Check out this link: http://energy.gov/sites/prod/files/oeprod/DocumentsandMedia/BlackoutFinal-Web.pdf It's a lengthy read but gives some good insights into the operation of the electrical power transmission grid.
  4. Gianoli

    Live tank X Dead tank breakers - specification differences ?

    If you are in a cold climate the dead tank breakers (DTB) utilize electric tank heaters to keep the SF6 gas from liquefying whereas the live tank breakers (LTB) utilize a mixed gas to prevent liquefaction. If you require black start capabilities LTB’s may be a better option for you in cold climates.
  5. Gianoli

    4160 versus 13,800V motors - Pro's & Con's

    Be careful with the larger motors feed at 5 kV. In order to realize the full rating of the motor you will likely be forced into using power circuit breakers rather than contactors. A typical 5000 HP motor at 4000 volts will draw somewhere between 585 - 640 Amps at full load. Depending on the...
  6. Gianoli

    120kV OCB Contact resistance

    Those values do seem extremely low. We maintain many types of transmission system breakers and even the 4000 Amp breakers had higher contact resistances than the numbers you recorded. The closest match we have in our system would be General Electric type KSO breakers. They are 1200 Amp, 138...
  7. Gianoli

    API 2026 Question ?

    API standard 2026 - "Safe Access/Egress Involving Floating Roofs of Storage Tanks in Petroleum Service" outlines, as the title suggests, a number of considerations prior to entering onto various types of tank roofs. My question concerns tanks with internal floating roofs. We have a number of...
  8. Gianoli

    Fault currents to high ?

    Thanks for the responses: ** What is interrupting rating of CB's today? 70kA? ** There are 32-138kV breakers rated at 80KA interrupting, 4000 Amp continuous. **What is the current rating required for 138kV breaker / switchgear if it has to handle 550MW - and how about the busbar and bus...
  9. Gianoli

    Fault currents to high ?

    I work for a utility that operates several large 138 kV systems. Several of these system have become too large in opinion. The most concerning is a 345kV/138kV substation sandwiched between a large urban area and a heavily industrialized area. The 138kV section consists of 16 outgoing circuits...
  10. Gianoli

    Voltage spikes experienced with a vacuum bottle breaker

    Wolf39: It is going to be hard to rank interrupting technologies in order of which tend to chop the most current. In some cases it is going to depend on the voltage level and specific breaker. Here are some general thoughts: 1. Air-Blast – For sure the worst. Keep in mind that all the breaker...
  11. Gianoli

    Voltage spikes experienced with a vacuum bottle breaker

    *Gianoli - Why is a contactor better than a circuit breaker in this regard?* I mentioned this in my previous post for a few reasons: A. The alloys used for vacuum interrupter contacts are always a compromise. They can’t weld together. They should have good electrical conductivity. They should...
  12. Gianoli

    Voltage spikes experienced with a vacuum bottle breaker

    relayman1000, I am going to assume when you use the term air blast circuit breaker you really mean air-magnetic circuit breaker. There are air blast circuit breakers but they were usually applied at the transmission circuit voltage levels. The ones used in medium voltage circuits were usually...
  13. Gianoli

    Vacuum Bottle integrity test

    Perhaps I need to clarify my position somewhat. The failure rate on these things is not low it's almost none existent. Do we have breakers/contactors/reclosers blow up? All the time. Probably a couple a month. Some have rodents enter the enclosure. Some get wet and blow up. Some get dirty then...
  14. Gianoli

    Vacuum Bottle integrity test

    Zogzog, "NETA recommends doing it "IF APPLICABLE ", whatever that means" You are not looking at the same NETA standard that I am what rev are you looking at? **I have the 2005 edition of the Maintenance Testing Specifications Guide. I can’t quote the exact section because I don’t have it...
  15. Gianoli

    Vacuum Bottle integrity test

    The company I work for has stopped all regular PM testing of vacuum interrupters years ago. We have thousands in service and the simple facts are that the number of failures we saw (basically zero) simply did not support continued testing. We still do some other tests but not vacuum bottle...