  1. FPelec

    Offshore power transformer YNd1 vs YNd11

    We normally use autotransformers for 230 kV / 69 kV and 400 kV / 135 kV transformers as well. While the advantage is less significant than in 400 kV / 230 kV units, we still find it beneficial.
  2. FPelec

    Offshore power transformer YNd1 vs YNd11

    I agree, there is no difference between Dyn1 and Dyn11. On the other hand, it seems like a strange setup to me. Why not use 400/230 kV and 230kV/66kV autotransformers instead? It would reduce costs and losses, and provide solid neutral grounding for the 66 kV network — which, in turn, would...
  3. FPelec

    Issues with transformer ester oils

    We’ve been using autotransformers insulated with natural ester (from various suppliers) since 2016, with tens of units currently in operation, and we haven’t encountered any major issues. These are typically 400 kV, 250 MVA units. It’s important to note that these transformers were specifically...
  4. FPelec

    Transformer clearance from Oil containment

    Hello 082399, if I remember correctly, IEEE standard 980 recommends that the oil pit extends at least 1,500 mm beyond any part of the equipment filled with oil. IEC 61936-1 reccomends instead that the length and width of the oil pit be at least equal to the length and width of the oil-filled...
  5. FPelec

    GIS Circulating Shell and Grounding Current

    Hello, In GIS installations, currents of similar order of magnitude as those in the phase conductors are induced in the enclosures. These induced currents become larger as the enclosure thickness increases; consequently, they tend to be higher in EHV switchgear. When multiple grounding points of...
  6. FPelec

    Wait to reenergize following lightning?

    Yes, SPAR is Single Phase Auto Reclosing, here is widely adopted on 400 kV and 230 kV lines; it's instead much less common on 150 and 132 kV lines. Our network code prescribes the following: "Automatic Rapid Reclosing (RRA) and Automatic Slow Reclosing (RLA) of transmission lines Automatic...
  7. FPelec

    Wait to reenergize following lightning?

    We normally adopt SPAR, so that the delay for re-energizing a 230 kV line after a lighting / flash over is about 0.5 to 2 s
  8. FPelec

    Voltage given from the secondary of the capacitive voltage transformer

    Each CVT includes an Electromagnetic Unit (EMU) whose primary winding is connected to the capacitive divider and has an output voltage of a few kV. If a CVT is energized from the low-voltage side (i.e., from the secondary winding of the EMU), the CVT will behave as a voltage source with a no...
  9. FPelec

    ACSR to ACCC without considering ACSS

    Hi, bacon4life, I expect the carbon fiber core (ACCC) solution to be significantly more expensive than ACSS but also somewhat lighter. In principle, I would not rule out other solutions using high-temperature aluminum alloys (ZTACIR or KTACIR) either. These latter options have far fewer...
  10. FPelec

    H-structure, Ductile Poles, Pupi Arms and Braces...Alternatives?

    Interesting question: given the prices I observe in my geographical area, if the required conductor has a relatively small diameter, for a 66 kV line, it might be cost-effective to use lattice or tubular steel supports (with steel crossarms and glass insulators or, alternatively, insulating...
  11. FPelec

    Three Winding Transformer Impedance Question

    Hi cyriousn, when specifying such a large transformer with the objective of limiting the short-circuit current to a reasonable value for CBs, a three-winding transformer is undoubtedly the best solution. We are currently manufacturing several dozen transformers for renewable energy collection...
  12. FPelec

    Surge arrester at the neutral point of HV transformer

    The surge arrester connected between the neutral and ground is used to ensure that, in the event the ground disconnect switch is open, no overvoltages exceeding the design specifications appear on the transformer's star point. This is typically employed when dealing with transformers with...
  13. FPelec

    345kV AC Submarine Cables

    Submarine ac cables have been installed for voltages up to 500 kV. A 400 kV double circuit submarine cables link, 42 km long, 2 x 1000 MW, has been in service between Sicily and Italy for about 10 years. A total of 1032 Mvar of shunt reactors are installed for reactive power compensation. A...
  14. FPelec

    500 Hz power transformer noise

    I would have also said that it was the fault of loose metal components/accessories on the tank, as suggested by prc; otherwise, the only thing that comes to mind is the presence of a very strong 5th harmonic in the load current.
  15. FPelec

    Maximum Transformer Impedance

    Hi kartracer087, I fully agree: split bus operation seems to me the most efficient solution. In the absence of other information, connecting 3 x 50 MVA transformers to the same 11 kV busbars, IMHO, is not a good solution. Even if it is possible to design 50 MVA 11 kV transformers with...