  1. FFP1

    Dry pipe valve in horizontal oreintation

    Existing 6in. DPV.........we need minimum 6 in. diameter. It does not look good at this juncture!
  2. FFP1

    Dry pipe valve in horizontal oreintation

    Are there ANY dry pipe system valves designed/approved to be installed in the horizontal position. We have a very unique challenge........horizontal dry pipe valve would be the best option; however, I cannot find any approved for horizontal oreintation!! Thanks
  3. FFP1

    Sprinkler Temp Selection for Boiler Rm

    You typically need to have 20 or more sprinklers which warrant testing to justify testing rather than replacing. I assume you have 8-20 sprinklers in the boiler/machine room.......might be more cost effective to simply replace all of the sprinklers (unless the two rooms have >20 sprinklers)...
  4. FFP1

    Missing suspended ceiling tiles

    It is really not a ceiling pocket because there are no vertical barriers to define the pocket. Also, NFPA 13 states the following regarding ceiling pockets: The total size of all unprotected ceiling pockets in the same compartment within 10 ft (3 m) of each other does not exceed 1000 ft3 (28.3...
  5. FFP1

    Missing suspended ceiling tiles

    Thanks cdafd!! The combination of NFPA 1 section 13.3.3.3 and NFPA 13 Section 8.15.4 along with the fastfacts article you provided should be enough for any reasonable person to realize they have a potential problem.
  6. FFP1

    Missing suspended ceiling tiles

    Maybe the attached picture will help........the walls in this room do not reach the steel deck above the suspended ceiling tiles (creates a huge space above the tiles in all directions). The sprinklers at the steel deck are not throughout; only installed directly above where the tiles have been...
  7. FFP1

    Missing suspended ceiling tiles

    Class II steel deck above. They changed from pendent to upright sprinklers at the roof deck for areas where the suspended ceiling tiles were removed. I would accept this arrangement IF we had vertical walls in the opening (it would be a large ceiling pocket!). NFPA 1 section 13.3.3.3 and NFPA...
  8. FFP1

    Missing suspended ceiling tiles

    I have a customer who has removed some of the suspended ceiling tiles (20ftx20ft area) in the middle of a large room. Elementary school occupancy. Steel deck above is 10 ft higher than the mineral tile ceiling. Pendent sprinklers remain where tiles remain. Upright sprinklers installed directly...
  9. FFP1

    Pump test

    The arrangement would be better with a gate valve directly upstream of the flow meter; therefore, you could eliminate the possibility of turbulent water flow in the vicinity of the flow meter. I am old school and I almost always use a test header if installed.........butterfly valves work just...
  10. FFP1

    Pump test

    I doubt the butterfly valve is the problem (as long as the control valve directly upstream of the fire pump is a gate valve; not a butterfly) The acceptance test should be completed using a test header (NOT using a flow meter). The test header results whoulc be used to confirm the flow meter is...
  11. FFP1

    FDC and Exterior Alarm

    Good point NJ1........details are important & I missed the mark on this one! I am not aware of any requirement for alarm devices in the vicinity of the system FDC.
  12. FFP1

    FDC and Exterior Alarm

    International Fire Code (2006) states the following: 903.4.2 Alarms. Approved audible devices shall be connected to every automatic sprinkler system. Such sprinkler water-flow alarm devices shall be activated by water flow equivalent to the flow of a single sprinkler of the smallest orifice...
  13. FFP1

    Water meter on dedicated fire service mains

    Commercial/Industrial facilities. I have a customer who is being charged a SIGNIFICANT amount for the water usage after the intial system fill and fire pump flow testing (intial acceptance testing activities).
  14. FFP1

    Water meter on dedicated fire service mains

    Part 1: Does anyone have any firm documentation which indicates whether or not public water departments can or cannot charge for water usage in dedicated fire service mains? Part 2: What percentage of dedicated fire service mains in your area of the country would you say already have public...
  15. FFP1

    ESFR - Anyone ever seen a Foam Water ESFR system?

    I re-read my post after reading LCREP post. Maybe I should clarify my comments.......I meant this comnbination would probably be VERY effective against fire incidents in general. ESFR systems and significant volumes of "flammable" liquids are generally a VERY bad combination...........too many...