Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by dynamo78

  1. dynamo78

    Valves' Cvs

    Sorry for the confusion for not having a well defined question. Based on your input, I was able to research what I want and needed to know. Thank you for all the inputs.
  2. dynamo78

    Valves' Cvs

    Thanks Moideen. Got it. By definition, Cv is the flow per 1psi PD across the valve. in this case, it's GPM. yeah, I agree with you. I should have included the PDs on the fittings too. I agree that the CV should be 15 as you have shown. Now if the Supply CHw side to the coil is closed, the bypass...
  3. dynamo78

    Valves' Cvs

    Well, The reason for being is that at 1 psi pressure drop the flow would be 8GPM, and to simulate the coil flow at 125 GPM and 15psi PD, the PD across the valve should be about 15psi PD too. right? Thanks Novice.
  4. dynamo78

    Valves' Cvs

    Hello fellow members, I just want to recall my HVAC knowledge if it still applies. Say, I have a cooling coil with 33Ft. PD @ 125 GPM, my old school knowledge says that I should a control valve with a CV of 8-9. Will that change if I have VFD in the chiller system? I appreciate any comment to...
  5. dynamo78

    Dry pipe system

    Thank You FP. Are you talking of Compressor "Performance Curve?
  6. dynamo78

    Dry pipe system

    Hi fellow members. I am being trained in the design of sprinkler and read in the NFPA 13 standard, for dry system, that if the air volume being delivered by the compressor is less than 5.5 CFM at 10 PSI, then an "Air maintenance device" is not required .I calculated the volume of the system to...
  7. dynamo78

    Fan static pressure

    @Lukai, Thanks for your input. I agree but I have limited resources to investigate the whole building and I got the assurance that ventilation system is ok meets the building requirement. That's why I came up with that simplistic solutions.
  8. dynamo78

    Fan static pressure

    I have to replace several fans that were installed in the 70s. I don't have any cat sheet or drawings to verify their performance and data, manufacturer closed shop. I know their CFM and actual Hp. I figured out that in order to verify the static pressures of each fan, I have to plot the CFM and...
  9. dynamo78

    Sizing Duct by Equal Friction Method?

    To the OP. Is the author "Stephen Kavanaugh? Thanks.
  10. dynamo78

    Condensate trap causing humidity issues?

    Beginner here chiming in. Hi dbill. Did you plot the coil performance on the Psychrometric chart? after shutting down the AHU, does the condensate flow freely to the drain? I mean while the AHU is operating does it hold the water in the pan then flows freely if it s off?
  11. dynamo78

    CH water calculations

    Thank you Bros. I really appreciate the inputs. Hope to return the favor later to other engineers.
  12. dynamo78

    CH water calculations

    @ Brony, Thank you and to the others. Till the next follow up question later.
  13. dynamo78

    CH water calculations

    @ Bro dbill74 "Your Qs equation is incorrect; correct equation is Qs = CFM x 1.1 x Delta T air" So based on your comment I cant use the equation: Qs= 500 x GPM x Delta T even for heating? I qualified this in my OP @BronYrAur Now, can I used the energy balance equation Qs (air side)= Qs (water...
  14. dynamo78

    CH water calculations

    Thank you Bro Trashcan man. I know this will be redundant but I'll confirm it anyway. If I was given the total load (Qt=Btu/hr) of a cooling coil then I can use the equation Qt=500 x GPM x delta T in determining the GPM for the coil. Thank you in advance for those inputs.
  15. dynamo78

    CH water calculations

    Can I used this equation to determine Chilled water GPM: Qt= GPM x 500x Delta T Qt= Total heat @ BTU/hr. Latent and sensible heat Delta T= Temp. difference between entering and leaving cooling coil. My point:Since the chilled water can handle sensible and latent load (Qt which is equal to: CFM...

Part and Inventory Search