Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by Denan

  1. Denan

    Old Siemens datasheet needed

    One more question: - the capacitor shown in the circuit har this data: 1µF +/-10% 1kV B25351-J1105-K000 I need to replace it as well. Found something here: https://www.elfaelektronikk.no/elfa3~no_no/elfa/init.do?toc=19344&pageSize=100&filterClause=COL_1%253D1%2520%25C2%25B5F but I am not...
  2. Denan

    Old Siemens datasheet needed

    Thanks for replays! I found a resistor with 50 W, so think we go for that. Space in the cabinet is not a problem. Yes I have found that at Siemens but those are newer models so I thought they are different. Assume that those resistors are not neded for new types. Am I right?
  3. Denan

    Old Siemens datasheet needed

    Hello, I am trying to find datasheet of an old Siemens vacuum contactor: 3TL 5100-1F 400A And / or Resistor: Siemens 470 Ohm, 110V 3 Ty S325-0E Attached is connection diagram. Actually, I am trying to find power rating for those two resistors, I need to replace them. Voltage between terminal...
  4. Denan

    Generator breakdown

    It is a CHP plant, used for greenhouse (is it called like that?).. I have asked to find out more about E/F elsewhere in the system, no replay yet.
  5. Denan

    Generator breakdown

    Hi, yes, we supplied the genset, and also control system, including protection. Not the switchgear etc.. About generatro beeing unearthed, that is common in the Netherlands, we have several plants like this one, and none of the generators are earthed in any way (only PE of course). But as you...
  6. Denan

    Generator breakdown

    Equipment was tested during commissioning. If it was tested after that again, I am not sure. Have no idea about those reports etc. you mention. I have already asked my colleagues at local office to ask the company that installed these breakers to check them all for possible faults. We will...
  7. Denan

    Generator breakdown

    Thanks guys for you coments! From the log it looks like both Gen. and Grid CB had multiple operations, apparently without anything initiating it. So, it may be that the generator got the damage on 03.sep. at 18:58, according to the Gen log. Breaker closed at 13:40 and did not open until 18:58...
  8. Denan

    Generator breakdown

    Here are logs from both protection units (generator and grid breaker) http://files.engineering.com/getfile.aspx?folder=537c5052-23cf-4fb3-a7a8-f55b76aa39c1&file=Gen_log.pdf http://files.engineering.com/getfile.aspx?folder=8553aeb6-9a3c-492e-ae95-bc80ac49a678&file=Grid_log.pdf...
  9. Denan

    Generator breakdown

    Hi, I wonder if the other breaker (grid breaker, utility breaker) might have some faults, because in log of prot. unit, we could see that this breaker did change status many times lately (before the fault) which is not normal there. Also, several times, there was an alarm we call Grid breaker...
  10. Denan

    Generator breakdown

    I try again... I have not been at site yet, I have not seen any pictures etc. Maybe during this week I will get a chance to travel there...
  11. Denan

    Generator breakdown

    Hi again, Now I got alarm list from SCADA, and it shows following alarms: Under frequency and under voltage, that is all. Unfortunatelly, alarm log from the protection unit dows not show anything from that day for some reason, nor several days around that day. I attach one more picture showing...
  12. Denan

    Generator breakdown

    Thanks guys for sharing your thoughts! Rasevskii, you are partially right, it is air cooled generator, driven by gas engine. It runs unattended, but it is in Europe (the Netherlands). It is around 6 years old. It could be dust as you say, I have been in the area before, and it can be pretty...
  13. Denan

    Generator breakdown

    Generator Sn=3021kVA, PF=0,8. CTs inside generator are 250/1A (apparently there is revised SLD which I did not find earlier). CTs outside of generator are 200/1 (for diff.relay)
  14. Denan

    Generator breakdown

    Thanks Erminio for the ides. We were also thinking of some kind of short circuit. When I first heard of the event, I also got info that it might have been that the breaker opened but got a flashover which may have caused this. I am still waiting for more info..
  15. Denan

    Generator breakdown

    Hi, Thanks for the input, I will ask for winding temp. record, not sure if it is available. I got information from site about the damage, I have not been there myself yet, it is in another country. I attach SLD for...

Part and Inventory Search