  1. coyney

    CT choice for transformer feeder

    You should not depend upon the primary side protection relays for a t/f secondary fault. The t/f ratio turns a secondary line/earth fault into a primary line-line fault. The secondary protection should cover for major secondary faults. The t/f will normally have specific protection e.g...
  2. coyney

    Capacitive Breaking Capacity of a Breaker

    Regardless of whether the load is inductive or capacitive the load is more onerous to switch when compared with a purely resitive load (i.e unity power-factor). The rated making capacity of a circuit-breaker is more arduous than the breaking capacity because of the potential XL/R ratio. If you...
  3. coyney

    Power Factor

    Low power factor = high inductive content of the load.
  4. coyney

    ACB vs MCCB

    Look at the IEC 947-2 definitions for Iuc, Icw, Isc & Ibc. ACB's: Larger and heavier More expensive Maintainable components Longer times fault for withstand capacity. Can be used with IDMT protection relays MCCBs: Smaller and lighter Please be carefull about the interpretation of fault...
  5. coyney

    Correct Terminology

    Correct terminology:- A generator is a DC device. An alternator is an AC device.
  6. coyney

    BREAKING CURRENT - MV CIRCUIT BREAKERS

    IEC 947-2 covers Circuit-breakers. This has several definitions with which you need to become more familiar. Icu = ultimate breaking capacity Isu = rated service capacity Icw = withstand capacity Imc = current making capacity. If you read the definitions and assess them they could be some...
  7. coyney

    ACB vs MCCB

    consider the fault-level at the transformer terminals by assessment of the HV system and the t/f reactance. Then consider the MCCB and ACB fault-making/breaking capacity. The down stream breakers/fuses need to checked to discriminate with the ACB/MCCB.