Thanks for the reply. I just purchased the 1735. I checked out the 1750 that you mentioned. Looks great, just a bit out of my budget right now. Maybe my next toy????
Anyone have experience using the Fluke 1735 3 phase power logger. I'm thinking about buying one and wanted to know what others thought about this product. I’m looking to use it for load flow studies in a mfg facility, energy conservation strategies and troubleshooting intermittent problems in...
Thanks for all the input!
We will be having a lighting vendor in anyways because we are considering LED lighting in some areas. I will surely ask that they make recomendations based on legal issues and proper lighting levels.
Not much daylight is available.
We are using a bunch of occupancy sensors. Problem is that we just had a major recontruction of how the production floor is set-up, so now there's too much lighting in some areas and not enough in others. Good suggestion though on the liability consideration...
I don't have too much experience in dealing with fluorescent lighting. I'm in an industrial facility with a few hundred 8 foot T8 fixtures. We're looking to save money by turning lights off in areas that don't need as much light. Can we achieve this just by pulling bulbs, or does that part of...
I'm baffled on something pertaining to selection of breakers for a new residential panel. In the NEC2008, the location requirements for AFCI protection have grown substantially. My question is this: With all the places that an AFCI or GFCI are required, where can you still use the standard 5 or...
The installation is below 600v.
Does a panel or wire being near an oil tank constitute as being "exposed to oil"? I agree I should check with the building inspector, but last time I asked him a question on a questionable item, he told me he was not an educational provider??
I have a question surrounding proposed location for a new panel board. First, I have a 275 gal oil tank for #2 heating oil in a home. The oil tank has a wall built around it with an access door. The inside of the wall is probably within 1 foot of the perimeter of the tank. This room is just...
I've been looking at used oil fired hot air furnaces for my home. I keep running into mobile home or trailer furnaces. What's the difference?? Can I put a mobile home furnace into my single family slab foundation house? Is one better than the other?
Questions on the control cabinet nameplate data i need to display on the cabinet:
2. For full load current rating of the machine, would I add the above mentioned motor as 8.2A or 2.21A?
3. Say this was the largest motor. Would I specify largest motor rating on this nameplate as 8.2A or 2.21A...
Thank you for the responses!
The application is an industrial machine with multiple motors/vfd's with one control cabinet. I sould have included more information as to where I was headed with this.
1.For the supply conductors to the machine, which rating would I use to calculate the load? I...
I have A VFD capable of running a 1 hp motor but will only be using a 1/2 Hp.
I'm running 208vac, 3 phase, 60 Hz
Motor nameplate states 2.21A @ 208vac
VFD nameplate states 8.2A @ 200-230vac
For the purpose of load calculations and sizing supply conductors, OCPD, and other peripherals, would I...
With all due respect, the 208 in most homes is single phase. If you looked at each of the sine waves, the phases would not be offset in time. You can have 208 with single phase. Hence the reason you see capacitors on the side of most appliance motors in the home to create the phase shift that...
Waross, as far as what I've seen, most 208vac single phase sevice to residential buildings is split phase not coming from 2 phases but one. The secondary coil in the transformer on the pole is split in the middle by the neutral. Neutral to one end of the coil would give you the 120 and end of...