Hi Everybody
WE have to connect a 600 KW, 600 V induction gen to utility now GPR is not a concern on Generation side as the maximum it can go is 600/Sqrt(3) but the secondary(utility) line 69KV , a single line to ground fault curent from them could be a concern. I asked the utility that I need...
Hi RCWilson,
A good observation for use of CT's through cables, could you advice where can I read about it conceptually. I would appreciat it, I got it what u said but not conceptually. This is not my question but interfering as I found it interesting.
Thanks
Hi
If any body could advice me, how to specify the rating of a motor contactor, I mean what the format stands for like in one of the threads I had
3RT10 15-1AB01 24V AC coil
how to read it.
# 2, What is the max, limit of current or voltage that we can use magnetic contactors, what vol or...
Hi I found this topic interesting, but a little confusing also, when we have a cut out and below that pothead in parallel with lightning arrester, So just wondering, is this true according to this arrangement the fuse will blow first for a lightening and a switching surge ?.
cheers!
I am a small fish but just a casual suggestion the whole story of earthing depends upon ground fault current which is then related to GPR and then touch and step potential. SO
we start it from back we get GPR and step and touch potential and see the value of resistance and if we realize that...
I got it now, so if I elaborate that means
if I have to calcualte to rating of capacitor for this induction generator and the utility has asked that it should opeate between .9 lag to .98 leading. So what
capacitor rating I need ?
This is what I think it should happen,
cos(fi)=.715...
Hey,
I need this too, I am modelling two induction generators in paralle and I have to calculate their three phase fault current and single phase fault current.
Hi Every body
I forgot to add some thing here
I have Locked rotor current= 1920 A
%FLC 458 referred to full load current 100 % load
code letter E,
I need to calculate the 3 ph fault current and single line to ground fault current, as it is an induction generator, am I supposed to model it like...
Hi Guys,
I got induction generator ratings from the manufacturer,
A little confusing needs help: It says KW=298.4 *** V=575 v
400 HP
LOAD 100% 75% 50%
EFFICIENCY% 94.00 93.80 92.70
POWER FACTOR % 71.50 66.20 54.60
AMPS 419.10 339.50 274.40...
Both generators are similar I think they had an impression that it is gonna be one generator, so they did not put the second one, from the diagram I see they have only two relays
SEL 551 and 547, I looked at the websites and I am also wondering, when we talk about bus protection that is a part...
Hi Guys,
I have been given a protection single line diagram for a
induction generator which will be connected to local utility.
The actual situation is that there are two induction generators but the diagram has only one, so I have to develop a new one with two, So my question is
Q #1 Should I...