  1. buddy91082

    Clearances to Manhole Access

    Thanks LowSpark. It is an existing manhole located outdoors. A "container" structure is being put in place 4'-0' above the manhole cover. So there will be access spaces around the manhole cover. I guess you can say access to the cover will be in a "void space" below the container structure...
  2. buddy91082

    Clearances to Manhole Access

    Hello all. I have a manhole with 600v conductors. Looking for clearance requirements above the manhole cover. NEC does not state clearances. Could not find clearances in OSHA. I will be installing a structure over the manhole and will be limiting clearance above the manhole. Thanks.
  3. buddy91082

    Single Pole, Molded Case Breaker Testing <600v

    So if I have a 3 pole, 100A, 480v molded case breaker, what is the procedure for testing? Do I need to remove the molded case enclosure to the breaker to perform a primary injection test and remove any shunt trips and then re-torque the breakers back into position? I have a manufacturer stating...
  4. buddy91082

    Single Pole, Molded Case Breaker Testing <600v

    This is a follow up to the thread below: thread238-444329 Would you normally perform primary injection testing on single pole, 15A/20A molded case breakers rated at 120v or 277v? (what you would see in a typical 100A/225A commercial panelboard that serves plug loads or lighting)? If not, what...
  5. buddy91082

    Impact of Motor Starting on Transformer Primary

    Hi all. This is a general question - when a transformer feeds a motor, does the primary side also see a voltage dip during startup, in ratio with what the secondary experiences? We have a light flicker problem when a motor starts and one solution is to install a transformer ahead of the motor...
  6. buddy91082

    Grounding Electrode Conductor Termination

    Per NEC 250.70, exothermic or mechanical lugs can be used to terminate grounding conductors to ground rod electrodes. Any benefit to either method? Thanks.
  7. buddy91082

    Low Voltage Primary Injection Test

    Is there a minimum size frame or trip rating to use primary injection testing on low voltage (<600v), molded case circuit breakers? NETA ATS does not define a minimum so one could assume it is across all frames and trips as small as 15A. Thanks. b
  8. buddy91082

    Led Driver Inrush

    One driver manufacturer stated inrush was not cumulative. After doing further research I looked at NEMA 410 - Performance Testing for Lighting Controls and Switching Devices. They describe the testing procedures for testing inrush. It is cumulative and looks like from Table 2 that the...
  9. buddy91082

    SKM Result - Negative Voltage Drop

    This is for 480v, 60hZ three phase feeders within a building 200'-300' long. The feeders are lightly loaded.
  10. buddy91082

    SKM Result - Negative Voltage Drop

    We are running a low voltage (<600v) drop study in SKM and are coming up with a few values with a negative voltage drop. Curious as to why the results might be coming up with a negative % voltage drop result on some of the buses and feeders and the negative % results means. Thanks. b
  11. buddy91082

    Led Driver Inrush

    Can anyone explain why driver inrush is not cumulative when having multiple drivers on a circuit. Is there a formula to determine the driver inrush when using multiple drivers? I have discussed the issue with several driver manufacturers and have not received a good explanation. Thanks.
  12. buddy91082

    Current in VFD

    Trying to determine how current changes when frequency in changed using a VFD. Voltage will change with frequency based on v/hz ratio. Hp change will be the cubed of frequency change. for simplicity, lets say HP = Volts x amps. If frequency changes 10%, voltage will change 10% and HP will be...
  13. buddy91082

    TCC Curves: What about events below .001 seconds?

    We have LED drivers with a rated inrush of 185 amps at 200 microseconds (.0002 seconds. We are trying to determine how many drivers we can place on a 20 amp, 120v circuit. The circuit breakers TCC curves start at .001 seconds. Also, the fuse TCC start at .01 seconds. What happens if the event is...
  14. buddy91082

    Break Horsepower vs Nameplate for Service Calculation

    Hi there. We are trying to right size our electrical service. We asked the mechanical engineer if there was any "fluff" in their pump and motor sizing. They said yes. For example, the calculated BHP on one pump is 23 bhp. They selected a 30hp motor (a 23% increase). We ere thinking we could...