  1. BrkfldEE

    Open CT secondary causing high impedance in primary?

    the pole discrepancy relay did trip the breaker on all poles. No we don't have any records of breaker status contacts to show that the one phase opened before the other 2. One more piece of evidence that was found was there was a second relay connected to a different CT winding that also showed...
  2. BrkfldEE

    Open CT secondary causing high impedance in primary?

    It is implemented by a protection relay. Sorry I can't post the schematic. This particular protection looks at the loss of current for pole discrepancy. My main question though, is if there was an open CT secondary, does it cause a high impedance on the primary of the CT, which would make the...
  3. BrkfldEE

    Open CT secondary causing high impedance in primary?

    In a high voltage substation there is an incoming source transmission line that connects to 2 circuit breakers, so the current from the incoming source splits between these 2 circuit breakers. One of these circuit breakers tripped due to a "pole discrepency", which means that one phase current...
  4. BrkfldEE

    using 2 taps on a multi-ratio CT

    The CT is an ANSI Multi-Ratio bushing type CT in a 115kV circuit breaker bushing. So I am hearing that using 2 taps on a CT at the same time will NOT work correctly.
  5. BrkfldEE

    using 2 taps on a multi-ratio CT

    stevenal, I am confused by your reply, are you saying that it is OK to use more than one tap on a multi ratio CT?
  6. BrkfldEE

    using 2 taps on a multi-ratio CT

    Will using 2 different taps of a multi-ratio CT work? Will it cause any problems?
  7. BrkfldEE

    Fiber Optic Cable Service Loop

    Is there a Code Requirement to leave service loops for Fiber Optic Cable? I have heard and read lengths of anywhere from 10' to 100' but I do not see anything in the NEC that explicitly says that a service loop of any length is required. Does anyone know of one?
  8. BrkfldEE

    noise induced on non-shielded wires in cable

    Thank you for sharing the common mode choke idea, I definetely learned something new with that. It will not work in this application because the negative wire is not run in the same place as the positive wire. However I will keep that in my back pocket for the future. I tried googling more info...
  9. BrkfldEE

    noise induced on non-shielded wires in cable

    I have a 125VDC control circuit that uses a non-shielded cable in a tray with AC power cables. There is 60 Volts AC being induced on a 125VDC wire. I know that the solution is to pull in a new shielded cable, but, does anyone know of a way to "drain off" this induced AC instead of pulling a new...
  10. BrkfldEE

    Standby battery bank discharge test

    We have multiple installations with varying ages from 1 year to 20 years. they are vented lead acid battery type. We had not been previuosly doing a discharge test.
  11. BrkfldEE

    Standby battery bank discharge test

    We have standby battery banks to provide DC power for our generating stations. Recently we started a monthly discharge test where we turn off the battery charger for five minutes to test the capacity/condition of the batteries. There has been some conflicting ideas on whether this is a good...
  12. BrkfldEE

    field discharge resistor - small hydro generator

    I am installing a Basler DECS-250 voltage regulator to provide field current to the rotating exciter. This AVR has a free-wheeling diode across the exciter field. Is the generator field breaker that I am installing un-necessary? Is there any advantages to installing this generator field breaker...
  13. BrkfldEE

    field discharge resistor - small hydro generator

    I have a hydro generator that is 12.5MVA, 13.8KV. The rated field volts and amps are 250V, 240A; and according to my datasheet the field resistance is 0.904 ohms. The rotating exciter has nameplate info of: 80KW, 250V, 320A, shunt wound. I am removing a field breaker that is in the exciter field...
  14. BrkfldEE

    Sizing Temporary Protective Grounds

    thread238-82004 Does anyone have a clear method to size temporary protective grounds? I have read IEEE 1246 and that doesn't seem to go into enough detail. I have read IEEE 1048 and it references some tables in ASTM F855-1997. However I can only get access to ASTM F855-2009 which doesn't seem to...
  15. BrkfldEE

    battery short circuit current

    I am working on evaluating our battery banks for arc flash hazards. The battery manufacturer gives a short circuit current rating of the battery, for example 2,044Amps. My question is, if I have 23 cells do I have to multiply the short circuit current by 23?