Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by bigdog

  1. bigdog

    Power Wiring for branch circuts

    Newfieboy What he is saying, that the wire going to the fuse can be a smaller gauge then that of the main line wire, which is 10 gauge. He telling me that a 16 and 14 gauge wire can be used up to the fuse.
  2. bigdog

    Power Wiring for branch circuts

    Your right davidbeach is it a control panel.
  3. bigdog

    Power Wiring for branch circuts

    Industrial panel and motor control circuits. Im using NFPA 79 and NEC.
  4. bigdog

    Power Wiring for branch circuts

    I have a stituation with one of my electrical engineers. The problem is with the design of his power destribution for branch circuits and the gauge of wire to be used. The rule-of-thumb that I was taught was that the wire going to the branch fuse needs to be the same size (gauge) as that from...
  5. bigdog

    DC Noise

    jbartos Can you tell the formula to calculate the capacitor. And is it wired in series or parallel with the brake.
  6. bigdog

    DC Noise

    I have a 3 phase induction motor that has a brake. I'm conrolling the motor with Mitsubishi VFD. We seem to be getting some noise from the brake when it is activated. I would like to know what kind of device can I use to filter the DC voltage. The control voltage the brake is 24VDC.
  7. bigdog

    Power taps

    Ok!! now I understand what your asking DanDel. Each sub-enclosure has it's own disconnect switch and primary fusing. The primary fuse for each sub-enclosure is between 15 to 10 amps.
  8. bigdog

    Power taps

    DanDel, Main feed conductor is 40 ft. long, the main fuse is a type J 60 Amp fuse, and voltage to be used is 208VAC, 3 Phase, 4 wire. I hope this is enough information.
  9. bigdog

    Power taps

    DanDel, What specifics do you require?
  10. bigdog

    Power taps

    I'm designing a conveyor system. On this system I have 11 sub-enclosures and one main enclosure. The power for the systeme is 208VAC, 3 phase, 4 wire, 60 Hz, 60 amps. Also there's 4" X 4" (hoffman) wireway (layin type) that connects all the enclosures together. The question that I...
  11. bigdog

    Interlocking Electrical Enclosures

    Evem though the sub-enclosures are single door (NEMA12) with latches. In other words it takes a tool open the door.
  12. bigdog

    Interlocking Electrical Enclosures

    I am working on a project that has one main electrical, and four sub-enclosures. The main houses the main disconnect and fuses. In the sub-enclosures theres fusing for the enclosure and motor controls (motor starters). My question is this; in the main enclosure the disconnet interlocks the...
  13. bigdog

    Power Line for conveyor

    I am design a part assembly conveyor. The conveyor will be running off 208VAC, 3 PHASE, 4 WIRE. The total length of the conveyor is about 90 feet long. The conveyor will have to split it in half (due to shipping and installation purposes). Thus, the power line will have to be broken, and I...
  14. bigdog

    COPPER AND ALUMINUM

    I have aluminum wire lugs and wnat to connect 6 AWG wire that is copper. Is it ok to combine the two materials.
  15. bigdog

    Liquidtight flexible conduit

    Can anyone tell (per NFPA) what is the maxium run length for liguidtight flexible nnmetallic conduit.