Recent content by arcflash99

  1. arcflash99

    Tap changer oil samplig

    You could send your samples to TjH2B. They have special tests they can run for OLTC's, OCB's and Regulators. The test uses a different set of parameters to diagnose the oil since it will be exposed to arcing. http://www.tjh2b.com/
  2. arcflash99

    Remote Racking Circuit Breakers

    Well we finally got our STR system commissioned. We opted to start with a Westinghouse DS-416 breaker software and installed a few cubicle kits to get practice for our upcoming turnaround where we’ll install another dozen or so. I am extremely impressed with this system. The portability (we...
  3. arcflash99

    Window CT on shielded cable

    We also had a false trip on a 12000 HP motor due to GF currents passing on the shields through a GFCT. Event: We had a VAC interupter partially fail on a feeder breaker at our main subsataion. The main sub also supplies power to the starter for the large motor. The result was there was enough...
  4. arcflash99

    Remote Racking Circuit Breakers

    One of our local sales reps actually brought one to our plant to check out. First off, at the time the unit was not approved by a NRTL. That is an immediate strike against our company policy. I suspect that reason for it is because it was manufactured in Australia. Second, we have quite a few...
  5. arcflash99

    Remote Racking Circuit Breakers

    Thanks Breakerboy. I have a system controller on order and a couple of kits to try out. While there is a substantial up-front cost. I believe it will be worth it. We have approximately 200-250 breakers to retrofit so it will take a few years. Next year we will convert the subs we are...
  6. arcflash99

    Remote Racking Circuit Breakers

    All of our technicians are instructed to hand crank the breaker to ensure it is inserted correctly, then connect the device and get out of harm's way to operate the RR device.
  7. arcflash99

    Remote Racking Circuit Breakers

    This particular unit has a torque limiter for the different manufacturer's breakers. It also counts number of turns as well as displaying "real time travel position". There are different transmissions for the different breaker types/ frames. king 101, how is the quality of the Safe T Rack...
  8. arcflash99

    G.E. Relay Instruction Books

    Not all of the instruction books are available on the web. I have had to request one through the website. I took a few days, but was worth it. They actually mailed me a hardcopy
  9. arcflash99

    Remote Racking Circuit Breakers

    Does anyone have experience with the remote racking device manufactured by Safe-T-Rack? http://www.safe-t-rack.com/ We are in the process of getting one to our plant to try one out and was looking for some possible pros or cons to the device. Thanks
  10. arcflash99

    Ventalation for a switchgear room

    If you do choose to close up the switchgear room, I would suggest air conditioning the building. As well as maintaining a positive pressure.
  11. arcflash99

    World's Largest AC Motor

    The refinery now belongs to someone other than Motiva. It was sold about 4-5 years ago to Premocor, not sure if they still own it. The two motors were part of a syn-gas plant that started when the place belonged to Texaco. I nkow they had some process issues for quite a while and couldn't use...
  12. arcflash99

    Motor 2X vibration problem

    If you want to separate the electrical possibility from mechanical, perform a "coast down" test. Monitor vib and shutdown the motor. At this point electrically induced problems should go away. Any mech problems should remain and degrade as the motor coasts down.
  13. arcflash99

    Motor PTC Thermistors

    They probably want to bring out the thermistor wires with the motor leads because on LV motors there usually isn't much room to machine another hole in the frame. As long as the rating of the insulation of the PTC thermistor cables are rated for the motor's operating voltage I wouldn't see a...
  14. arcflash99

    An interesting set of Voltage Measurements

    The phase to ground problems is what started our investigation into the phase to ground unbalances. All motors, MOVs, and other 3 phase loads have been working just fine. Thanks for the info
  15. arcflash99

    An interesting set of Voltage Measurements

    David, I don't understand how I can have an offset neutral with a delta secondary. If it is offset, how does one correct it?