Have a 16 ft heavily loaded PSL beam, simple span. Say I want to extend the beam a foot or two to simplify construction, and infill that foot or two. Will the moment cause by that cause excessive uplift or buckling of the trimmer studs? Or should deformation be low enough that it can be neglected?
I don't usually work in freezing locations, but currently working on a house with a 45 degree metal roof, no drift or unbalanced load, just straight 30 psf sloped slippery roof snow load throughout.
1) Is a snow fence really needed on this roof?
2) If we use a snow fence at exit/entries (a...
Oh you're right. I hate how convoluted the NDS is when trying to figure out which factors to use on which properties. for which sizes. It's like a giant 3D matrix scattered around multiple chapters of multiple documents.
A window header could be one. I mentioned a skewed purlin in my OP (ignoring diaphragm action to be conservative). 3.9.2 applies to bending and compression as well and looks a bit easier to plug into a spreadsheet than 15.4.1
Strong axis = fb1
And it would make sense to calculate F_be for...
Wondering if anyone has an answer to this.
Biaxial bending is in chapter 3.9 of NDS. It has F_bE in the denominator of the last term. Go back to section 3.3.3 and this variable is a factor of some other variables:
1) It is a factor of the slenderness ratio, which is otherwise used to calculate...
There is enough thickness, it is a 16" wide by 20" thick footing.
10" is the maximum epoxy embedment and that is not strong enough for overstrength or ductility.
Originally we assumed a 12" thick footing, and specified a new 16"x16" footing below with t&b rebar. Now that we know the existing...
Wonder how you all detail a holdown anchor through an existing footing.
Do you bolt it directly to the bottom of the concrete and allow deformation or crushing at the rough surface? Do you extend a distance below the footing and cast it in? Is there a need to use rebar or does a block of plain...
The slab will be exposed as mentioned in the title. The anchor bolts have to be concealed. I suppose we could use leveling nuts and grout at the concealed steel columns. I was thinking it might be difficult to fit it within 5.5" stud width.
Looking more into this, I am learning there are other...
Designing a house. There are 8 concealed steel columns and 2 exposed wood columns at the interior slab. Many of the steel columns act as wood shear wall end chords as well as roof support (we have snow load at this location). Originally I have been designing this with continuous footings...
We always require rebar shop drawings, no matter the size of the project. On small projects, we often don't see any or expect to see any. Sometimes we don't even get steel fabrication/erection drawings. And sometimes when we do, the shop is so small that the "shop drawings" are just copies of...
I'm coming across this same issue as in this thread. Shear capacity with the hole is greater than 2/3Vp.
https://www.eng-tips.com/viewthread.cfm?qid=454419
I'm wondering why this triggers a web buckling check, even if there is zero shear at the hole.
I have a compact W8 and a 3 inch hole. It...
Yes! Table 9, installed on top of concrete on metal deck, 1/2" anchor with 3" nominal embedment, 1 3/4" minimum edge distance.
Interesting. The Hilti ESR has a note below the "top of concrete fill on metal deck" table, stating that for other diameters and embedment depths, refer to the other...