  1. 7anoter4

    Gas tight cables - Gel as filler

    See-for information only: gastite_di_guide PDF (www.gastite.com)
  2. 7anoter4

    Txf DGA sampling question

    See-for information: tv0009-fa-oljeprøve-2019_a4_engelsk PDF (new.abb.com)
  3. 7anoter4

    70:250.30(A)(1) Exception 2

    In my opinion, the art.250.30 A(1) System Bonding Jumper requests a single SSBJ at the source enclosure, and Art.250.30 A(1) exception 2, permits 2 SSBJ: one at the source and the second at the disconnector side. In this case, we may not connect these two SSJBs with a bonding wire in order to...
  4. 7anoter4

    Protection Functions

    In my opinion all the symbols except Ursd and df/dt are IEC 60617 protection graphical symbols. Ursd may be Residual Voltage Relay and df/dt it has to be rate of change ROCOF relay .
  5. 7anoter4

    Buried Earthing Grid in Concrete Foundations - German Philosophy

    See also BS 7430:2011 9.5.8.5 Structural steelwork
  6. 7anoter4

    iec 60364-5-52

    My edition of IEC 60364-5-52 standard it is from 2001 In this edition Annex B is for information, only. Also, in the last edition [of 2024?] as I saw, Annex B it is informative only. So, the actually normative part is still A. On A 20 it is written: NOTE 3 Values are given for vertical spacings...
  7. 7anoter4

    What is positive to negative sequence coupling and negative to positive sequence coupling ?

    See: EPRI AC Transmission Line Reference Book—200 kV and Above, Third Edition Chapter 2: Electrical Characteristics of Conductor Configurations and Circuits
  8. 7anoter4

    Powerfactory zero sequence voltage calculation

    First, I calculated the primary phase-to-phase angle and I took for secondary phase-to-neutral the same angle[see the sketch]. Then I calculated the secondary phase-to-phase voltage using these phase-to-neutral secondary voltages, changing the absolute value -only-in order to create a...
  9. 7anoter4

    Powerfactory zero sequence voltage calculation

    If we recalculate the Delta phase-to-phase voltages using voltages phase-to-neutral the absolute value is not 400 V but 402.7 AB, 411.4 BC and 407 CA. That means the phase-to-neutral voltages are different. If Powerfactory software may approximate these different phasor values in order to reach...
  10. 7anoter4

    Ground(earth) continuity conductor (ECC) within substation

    If the cable run in trefoil formation -as per IEEE 575-for a rated load -up 1000 A the built-up voltage it will be less than 3 V . In case of short-circuit up to 90 kA- the voltage will be 250-300 V In flat formation-one feet distance, not cross bonding-for rated load may be 10 V, but for 90 kA...
  11. 7anoter4

    open delta 3 phase voltages - 2 single phase transformers

    If there are 2 single phase transformers 240/120 you'll get only 120 V between X1,X2,Xo ,if instead of H1 and H2 connected in the middle [short-circuit!] you'll put H3. In order to get "high point" you need 3 transformers, but for only 104 V. For 208 you need 240 V secondary [not primary!]
  12. 7anoter4

    110/33 kV transformer and REFCL for metro line

    https://distribution.epri.com/wildfire/public/wildfire-tech-database/fault-energy-reduction/refcl/
  13. 7anoter4

    Elevated cable trays - when could these be considered subject to physical damage and unsupported tray cable not allowed per the NEC?

    In order to protect the cable, from cable tray up to connected equipment, you have to keep the minimum required in NEC Art.300. In a power station -mainly in a machine room-it is recommended to run the cable from cable tray up to maximum 6 feet from the equipment in a rigid conduit-usually rigid...
  14. 7anoter4

    Fault Current Analysis

    If the tertiary winding is grounded, then the total impedance of the system decreases.