Recent content by 3cio

  1. 3cio

    Fire protection for hydroelectric plant tunnel under construction

    Hello! Good day! As mentioned, the project is a Hydroelectric Power Plant. I suggest you go through NFPA-851(2010) & NFPA-850 (2015). These recommended practice are good start. NFPA-851 chapter 8 (Fire Protection for the construction Site) Hope this helps, PAtrick
  2. 3cio

    Sprinklers Around Walls Exposed Sprinklers

    Hello, Good day! I think, you can upload a simple drawing in order to clearly address the situation. Thanks, PAtrick
  3. 3cio

    Outdoor Storage of Chemical Products

    Hello! Good day! These are my suggestion only: Our concerns are as follows: a) Is there any chemical product from the above, which shall never stored outdoor? you could go through the Material Safety Data Sheet with reference on the properties of the chemicals, and you could refer to NFPA-30...
  4. 3cio

    Deluge Valves for Transformers Room

    Hello FPE22! Good day! With regards to: "Wetting the transformer having fire is what we're intending to do. It's a waste to ruin the other transformers having no fire." Please be noted that as you mentioned, they are installed within the same room and there are no fire barriers between each...
  5. 3cio

    Dry-type transformers fire protection ?

    Hello! Good day! just an idea. I suggest you to go through NFPA-13. Hope this helps, PAtrick
  6. 3cio

    NFPA code for AHU room used as a plenum for Fresh Air?

    Hello Almogavar! Good day! Just an idea; I suggest you go through NFPA-90A. Hope this helps, PAtrick
  7. 3cio

    Mixing ordinary and intermediate temperature fire sprinkler heads in light hazrd occupancy

    Hello! Good day! In my opinion; Contractor could say that NFPA doesn't prohibit him to do so as you said, but installing same type of sprinkler is also as per NFPA. Therefore, owner could insist the same and the contractor should follow. Reason is: By definition, AHJ is an organization...
  8. 3cio

    Mixing ordinary and intermediate temperature fire sprinkler heads in light hazrd occupancy

    Hello! First, I assume that NFPA 8.3.2.2, 8.3.2.3, 8.3.2.4, 8.3.2.5 does not met with regards on your situation since you said that intermediate temperature sprinkler is not required. Temperature ratings of a sprinkler are used for the following; A) To keep sprinklers from operating...
  9. 3cio

    NPSH

    Thanks TD2K. I use the chart (flow vs. pressure drop vs. size) provided by the manufacturer. Yes, this drop is base as when the strainer is clean.. Regards,
  10. 3cio

    FM 200 Nozzle location

    Hello Guys, Good day! We have a scenario in which I would like to hear a comment or an opinion from you guys. The thing is, in the Manufacturer's Manual, it is mentioned that the nozzle should be atleast 300mm max. from the ceiling. In our current site condition, it is not possible since we...
  11. 3cio

    NPSH

    Hello Guys, Good day! When we calculate for the NPSH with Strainer installed, is it correct to assumed that: NPSH = Atm. pressure + Static Pressure - Vapor pressure - Pipe/Fittings/Valves pressure loss - Strainer pressure loss The thing is, I am thinking that A pressure drop shall be...
  12. 3cio

    Foam Chamber

    Hello Experts! Good day! Iam currently designing a foam chamber (particulary ansul). In the catalogue, it is mentioned the flow range between 40 psi to 100 psi which corresponds to cetain K-factor. The thing is, the incoming pressure at the flanged inlet of the foam chamber is 130 psi. In...
  13. 3cio

    Pressure at hose valve

    hi! I think if the system is to be provided with centrifugal fire pump, it should be more than 40psi as per NFPA-20 clause 4.8.2. As per AHJ requirement in my previous project, they are always requiring class II system in every building as a first line of defense. Tjen, 4.5bar is required...
  14. 3cio

    Fire Fighting System Design

    Hi! 1. As mentioned in NFPA 20 handbook, we could take a rule of thumb of 1% of FP capacity. Sometimes, we calculate for the leakage rate if we have a large underground system or we select it as a one sprinkler flow. Whichever is higher. 2. There is no requirement of providing two jockey pump...