This Post is regarding selection of control damper .
Duct pressure classification given as 2 inch w.g..
Usually control damper rated for the maximum pressure and maximum velocity, beyond which damper may not performed the indented purpose and hence the operating condition shall not exceed...
ASHRAE standard 170 specify operation theater temperature should be 68F and RH (30 -60%). however, in may case, indoor design condition is 68F DBT and 50+/- 5% RH. I am using E20 form to calculate thermal load for the operation treater. To selected the apparatus dew point I could not find the...
why design profile temperature for month of july and august are same for MINOT IAP in HAP 5.11https://files.engineering.com/getfile.aspx?folder=b895a188-1765-4aad-8518-0a998efd6baa&file=SSN2587.tmp.pdf
Dear member,
I am designing process equipment enclosure for the following design condition
Annual cooling (DB/MCWB) – 91 F / 69.2 F and inside to be maintained at 1040F
Annual heating (DB) – (-17.7 F) and inside to be maintained at 50F
Evaporative colling (WB/MCDB) 73.5 F / 84.4 F and inside to...
I am new to HVAC industry and assigned task to design air conditioning system for 33 KV substation wherein switch gear room has to be maintained positive pressure of 30Pa. Equipment heat gain is of 250kw and room to be maintained less than equal to 25C deg and RH of 75% max.my question is how...
Dear member,
It is general practice to provide 3 mtrs Acoustic insulation in supply and return duct from AHU. Irrespective of AHU capacity. i.e CFM. However, low capacity AHU/FCU/Split Ducted unit may not required upto 3mtrs acoustic insulation. Hence, on what basis acoustic insulation shall be...
I come cross damper schedule (design by others). They are mention minimum flow rate and maximum flow rate, min velocity, max velocity, and static pressure drop. i.e AHU supply flow is 4695 l/s. AHU Machine – VAV type , Air distribution by using Variable air volume box . Fire Damper schedule. Min...
Mr. PEDARRIN2
Thanx for prompt useful advise. i will elaborate more to have better understanding of my problem. as i mention that 7 story building , strom water from roof , waste water and sewage up to level 1 are directly going to existing manhole at level 0.from level 0 ,level -1 and level -2...
Dear member,
My new building(area 355m x 125 m) of 7 story and 3 story (level 0 level -1, level -2) below the grade and used for car parking purpose. Dry – wet well arrangement (located in level -2) is to be considered to dispose parking drain, to avoid flooding. Rain fall intensity is in my...