Hi,
Thanks for sending link.
As per my knowledge;
Advantages of Sweep response method are;
1) High signal to noise ration. This comes from using filtering function of the network analyzer to remove broadband noise.
2) It is possible to use a finer freq. resolution at low freq.
3) Only one...
Dear All,
I am just starting new thread with some question for transformer diagnostic by using frequency response analyzer.
1) What are the difference between low impulse & sweep freq. method?
2) Is the sweep freq. method is more precise than impulse method?
3) FRA & Tan delta test are...
Hi All,
I am just starting new thread. Today, most of the protection engineers know about numerical transformer differential prot. relays & most of the relays are having three SLOPE characteristics (i.e. 7UT612, P632, RET531,T60 etc.). What should be the criteria & considerations to set third...
Hi,
CTZM is relese & earlier it was always connected with low voltage circuit breakers which had been supplied by GEC ALSTHOM. Now they have stopped manufacturing even they are not making new releases. you can replaced by new one microprocessor based L&T make (SR21) or SIEMENS make (7series) or...
Hi,
Electromechanical, static & numerical relays required to installed in Air condition room? or only static & numerical relays reqd. to installed in air condition room?
Is it reqd. to installed relays in air condition room where ambient temp. is not more than 35 to 40 degree?
What should be...
Hi,
I forgot to say one more thing in my earlier discussion;
ETAP, PSS/E, EUROSTAGE, SIMPOW, SKM, CYME etc. Electromechanical Transient Programs & EMTP/ATP, PSCAD/EMTDC, NETOMAC etc. Electromegnatic Transient Programs.
Electromechanical Transient Programs are good to study for Power system...
Hi,
Basic calculation is;
I have assumed; it's 3-ph symmetrical fault current = 9000A
Primary voltage = 13.2kV
Secondary voltage = 208V
Through fault current refelcted on Primary side = (208*9000) / (13.2*1000) = 141.81 Ampere
Is this three phase TR or single phase? If it is three phase then...
Hi,
Sorry,i am late
I know ETAP power station software is having module or option that allows relay testing, with direct communication between software & DRT6 or ART3 (ISA make) instruments on desired freq. sampling rates (say; 2kHz, 5kHz, 10kHz or 20kHz etc.), but again i am saying it's a ETAP...
Hi,
Earlier, OMICRON & SIEMENS was tied up & OMICRON were started to manufacturered instruments for SIEMENS only as per the guideline of SIEMENS.
SIEMENS has made SIGREA software then OMICRON has used same platform for Advance Transplay.
Thanks
Thanks 521AB for information.
If i need to enter relay settings manually (Read from relay front screen or setting software) in "testuniverse" software & it is creating XRIO file then what it does really make any sense? My understanding is; this feature is similar to looks like as a ISAWIZARD...