Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Fuzzy Logic Tuning

Advanced Control

Fuzzy Logic Tuning

by  controlnovice  Posted    (Edited  )
DeltaV's Fuzzy Logic Controller (FLC) has three tuning parameters. I'm not sure about other manufacturers. They are:

% Error
% Change in Error
% Output

% Error: Very similar to P in PID. It looks at the error between setpoint and actual value. The parameter is in % of full scale of your process value.

% Change in error: How fast the process is approaching setpoint. This is also in % of full scale of your process value.

% Output: When the process value differs more than the "% Error" and the process value is heading in the 'wrong' direction (away from setpoint) by more than the "% change in error", then the output will change by the amount in this parameter. But, if the % Error or the %change in error is below the set parameters, the the fuzzy logic kicks in to determine how much and which direction the output will go.
Register to rate this FAQ  : BAD 1 2 3 4 5 6 7 8 9 10 GOOD
Please Note: 1 is Bad, 10 is Good :-)

Part and Inventory Search